I have a weirdly designed house.

The attic in the lean-to addition has 2x6 joists (actual 2x6 - old wood). The joists sit directly on top of the wall framing for the ouside wall, and extend outward from there. They're notched to sit flat on the outside wall header. - there's less room for insulation there, as teh joists are no longer the full six inches.

There was never any room for both insulation and ventilation, so we have a 'hot roof'. It was created using three sheets of XPS foam sandwhiched together, and sealed with copious amounts of canned sprayfoam.

In the winter, we saw striping on the roof when the first snowfall happened, so we were thinking of getting a DIY sprayfoam kit and adding more insulation - and encapsulating the joists.

The issue is where the roof joists meet the outside wall - there's no way to add insulation to those without lowering the ceiling on the entire roof.

How big of a thermal bridging issue will it create if I sprayfoam the joists on the entire roof, except at the bottom?

Asked by Anders Ufland
Posted Tue, 07/15/2014 - 23:56
Edited Wed, 07/16/2014 - 05:43

Tags:

4 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Anders,
Q. "How big of a thermal bridging issue will it create if I spray foam the joists on the entire roof, except at the bottom?"

A. The thermal losses will be relatively small from the perspective of their effect on your energy bills, but could cause problems with ice damming. I would go ahead with your plan, and monitor the ice dam situation.

If you don't want to lower your ceiling, but you still want to improve the thermal performance of the roof, another option is to install rigid foam above the existing roof sheathing. Of course, if you do that, you will also need to install new roofing.

Answered by Martin Holladay, GBA Advisor
Posted Wed, 07/16/2014 - 05:42
Edited Wed, 07/16/2014 - 06:13.

2.
Helpful? 0

I was worried about condensation as well - Is there a chance of condensation on the underside of the foam (or worse, between the roof and the foam), if not enough insulation is applied?

Answered by Anders Ufland
Posted Wed, 07/16/2014 - 09:44

3.
Helpful? 0

Anders,
The method you used to insulate your rafter bays is called the "cut-and-cobble" method. Here is a link to an article with more information on the method: Cut-and-Cobble Insulation.

Q. "Is there a chance of condensation on the underside of the foam (or worse, between the roof and the foam), if not enough insulation is applied?"

A. Yes, which is one reason why many experts advise against using the cut-and-cobble method for unvented cathedral ceilings. The article I linked to includes a few anecdotes of failures.

To the extent that you are successful at reducing air leaks and cracks with your two-component spray foam kit, you will be lowering the risk of your cut-and-cobble assembly.

Answered by Martin Holladay, GBA Advisor
Posted Wed, 07/16/2014 - 09:59

4.
Helpful? 0

Dear Anders,
While spray polyurethane foam is a great solution for air sealing and insulation, I would strongly encourage you to find a qualified contractor to apply the product. You can find some additional guidance about the safe use of these products here: http://polyurethane.americanchemistry.com/Resources-and-Document-Library...

Answered by Richard Skorpenske
Posted Sun, 07/20/2014 - 13:52

Other Questions in Green building techniques

In Energy efficiency and durability | Asked by Noah Byler | Jul 23, 14
In General questions | Asked by Robert Shelton | Jul 25, 14
In General questions | Asked by Roger Berry | Jul 24, 14
In PassivHaus | Asked by Scott Tenney | Jul 24, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!