Dense-Pack Cellulose Cathedral Ceiling

My roof (zone 3B) needs insulation, but between Martin's concerns and the inexperience of the contractors in this market, I am conceding that 5" of polyiso foam isn't going to happen. I think that 3.0" nail base (R15) can though (with taped seams). I'd like to get closer to the code minimum of R30 for the assembly. I would rather not tear out the finished interior vaulted ceiling (cedar shingles on battens on felt paper, I know, strange), but the lousy interior air barrier (i.e. the felt paper) concerns me. Given that 4" of dense-pack cellulose is air permeable, how big of moisture risk would I be taking in this climate with this assembly?

Asked by Keith Richtman
Posted Aug 14, 2014 3:44 PM ET

Tags:

3 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

You're talking about putting R15 continuous over the roof deck, and then re-roofing over that? If so, you should be fine--do the exterior work first, including the roof cover, and then have an insulator strategically remove shingles on the interior side and dense-pack the rafters. If there is currently venting at the eaves you might need to close it off.

Answered by David Meiland
Posted Aug 14, 2014 5:04 PM ET

2.

In a zone 3 climate you need to have about 13% of the total center-cavity R to be exterior to the roof deck for dew point control if you had an air-tight 5-perm interior. Doubling or more that would prudent if the interior side can't be made air-tight. If the interior tar-paper is in pretty good shape and only torn or leaking in a few spots (rather than falling apart, crumbling into flakes everywhere) it will be a sufficient vapor retarder once you dense pack it, so you may not even need to double it for dew point control. (#15 felt runs under 5 perms when dry.)

At 4" true depth(as opposed to a milled 2x4, which is 3.5") the most you'll get out of dense-packed cellulose is about R15. A 3" nailbase will probably be OK, but know that you're going to be relying a bit on the buffering capacity of the cellulose (which is fine- it works.) It's lower risk in zone 3B than it would be in 3A, but it would probably still work in 3A.

IRC 2012 code minimum for zone 3 is R38, but that is for insulation thermally bridged by joists/rafters. The performance of your continuous nailbase at R30 total center-cavity R will be comparable or better performance than a well-implemented R38 joist/rafter batt-job.

Answered by Dana Dorsett
Posted Aug 14, 2014 6:13 PM ET

3.

Thanks guys!

Answered by Keith Richtman
Posted Aug 14, 2014 7:03 PM ET

Other Questions in Green building techniques

Non-typical insulation of barn / garage

In Energy efficiency and durability | Asked by James Williamson | Mar 22, 15

Fresh air distribution for hydronically heated house?

In Mechanicals | Asked by John Charlesworth | Mar 26, 15

Insulating scissor truss

In Energy efficiency and durability | Asked by Tom Smith | Jul 19, 14

Attic insulation reality check

In Energy efficiency and durability | Asked by Nathaniel G | Mar 26, 15

Old house, wet brick

In Energy efficiency and durability | Asked by Chris Ermides | Mar 26, 15
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!