Helpful? 0

What are the chemicals used in GeoExchange?

Specifically, what are some common fluids used for circulation through the loops, and why? what properties make these liquids good for this purpose? Also, what are the refrigerants used for heat transfer from the liquid being circulated to the heat pump?

Asked by Louisa Murray-Bergquist
Posted Tue, 01/08/2013 - 19:11

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 1

Louisa,
First of all, the word "Geoexchange" is a registered trademark used by an industry organization called the Geothermal Exchange Organization. The technical name for the type of heating and cooling system that your are thinking of is a ground-source heat pump.

There are many types of ground-source heat pumps. Some have an "open loop" that circulates pond water or water from a vertical drilled well. Others have a "closed loop" that circulates ordinary water or a water and antifreeze solution through horizontal looped tubing (tubing buried in a trench) or through vertical tubing (tubing inserted in a drilled vertical borehole).

If antifreeze is used -- it is optional, not required -- the two most common products are ethylene glycol and propylene glycol. Of these two products, propylene glycol is less hazardous to humans if accidentally consumed.

Still another type of ground-source heat pump -- a so-called direct exchange system -- circulates a refrigerant through buried copper tubing. The heat pump industry uses several different refrigerants; if you want to know the specific refrigerant used in a system that you are considering installing, contact the equipment manufacturer and ask the company which refrigerant they use.

For more information on these systems, see this article in the GBA encylopedia: Heat Pumps: The Basics.

Answered by Martin Holladay, GBA Advisor
Posted Wed, 01/09/2013 - 08:39

Other Questions in Green products and materials

In Green products and materials | Asked by joe k | Jun 18, 13
In General questions | Asked by Eric Mikkelsen | Jun 18, 13
In Green products and materials | Asked by Andy Chappell-Dick | Jun 11, 13
In Green building techniques | Asked by barbara matheson | Jun 18, 13
In GBA Pro help | Asked by tami weathers | Jun 18, 13
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!