What should I do to make sure an older boiler is venting properly when I seal up the basement?

I am sealing up the basement of a 100-year old multi-family with a 40+ year-old steam boiler. Prior to this work there was a lot of airflow intrusion which is now being reduced. How do I make sure that the boiler is venting properly up the chimney and there are no internal leaks? Is there anything I can do to introduce heat savings on the venting end of the cycle without changing out the boiler?

Bob

Asked by Bob Rueter
Posted Tue, 03/03/2009 - 19:53

Tags:

3 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Robert,
Atmospherically vented boilers require an adequate amount of combustion air, as you know. Code requirements for combustion makeup air vary depending on whether a home is built to average construction or tight construction — loosly defined terms, unfortunately. An HVAC installer or home-performace contractor should be able to test the operation and safety of your equipment to determine whether adequate combustion makeup air is available. If you can't determine this by yourself, it's time to call a professional.

If combustion is incomplete and venting is imperfect, your boiler could release carbon monoxide into your home. It's not worth guessing on the details.

Answered by Martin Holladay, GBA Advisor
Posted Wed, 03/04/2009 - 14:07

2.
Helpful? 0

Robert,

I have been look at products from this company for my own house: http://fieldcontrols.com/cas.php

I have no idea how well they work, and would rely on expert advice myself. I have heard that there can be problems (particularly at start up) with the boiler pulling in completely un-tempered air.

-Tobias

Answered by Tobias Richon
Posted Thu, 03/05/2009 - 22:22

3.
Helpful? 1

The average boiler lasts 30 years. Perhaps a new ModCon boiler with sealed combustion and no more worries.

To make a one hundred year old house tight enough to starve a boiler is very difficult. A combustion analysis by a qualified heating contractor would be wise however.

www.badgerboilerservice.com

Answered by Morgan Audetat
Posted Mon, 05/18/2009 - 17:40

Other Questions in Mechanicals

Is this furnace venting/leaking problem as bad as it looks?

In Mechanicals | Asked by Nathaniel G | Dec 20, 14

How to handle SE/SW orientation? And any experiences with Richlin windows?

In PassivHaus | Asked by Ryan Griffin | Sep 29, 14

Wet OSB - how much water can it take?

In General questions | Asked by colleen1 runyen | Dec 17, 14

Sensors in the house envelope

In Energy efficiency and durability | Asked by Karl Overn | Dec 21, 14

Airsealing an attic

In General questions | Asked by Dan McGonigle | Dec 21, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!