Dedicated ERV system and Bathroom Exhaust
We are designing a dedicated ERV (recouperator) duct system in a high efficiency remodel. The question has arisen regarding the bathroom exhausts and whether we can utilize the ERV exhausts in each bathroom and a booster switch (dual function timer) in lieu direct vent bathroom exhaust fans. Thoughts? Ultimateair does not to take a strong position on it in their literature.
Asked by Patricia Shields
Posted Mon, 01/02/2012 - 17:01
Posted Mon, 01/02/2012 - 17:01
Tags: Mechanicals
Other Questions in Mechanicals
In Mechanicals | Asked by Jane Smith | May 24, 12
In Building Code Questions | Asked by michael maines | May 23, 12
In Energy efficiency and durability | Asked by Victor Burgos | May 23, 12
In Energy efficiency and durability | Asked by David Slade | May 21, 12
In General questions | Asked by Robert Hronek | May 23, 12
Yahoo
Technorati
Google
Facebook
Delicious
Digg
StumbleUpon
Reddit

Yes, you can do this, but you don't necessarily have to install the booster switches. Design these exhaust branches to the code required continuous exhaust (typically 20cfm for bathrooms), then install and test/balance the airflows.
Posted Mon, 01/02/2012 - 18:22
Here is a link to a previous discussion. I would agree with John above. Many HRV/ERV's offer the ability to increase fan speed when necessary via a point source switch.
http://www.greenbuildingadvisor.com/community/forum/mechanicals/18285/hr...
Posted Mon, 01/02/2012 - 18:56
My vote is to stick with the ERV -- don't install separate exhaust fans in your bathrooms.
Posted Mon, 01/02/2012 - 19:52
You maybe required by code to have seperate ventilation for bathroom due to contamination build up in an air to air exchange ventilator, which could cause sick building sydrome or mold propagation. check with local building code and or International Residential Code
Posted Tue, 02/28/2012 - 19:49
Thom,
There are no such prohibitions in the International Residential Code, to the best of my knowledge. Please cite a relevant section.
According to section M1507 of the 2006 IRC, bathrooms need at least 50 cfm of intermittent exhaust ventilation or 20 cfm of continuous exhaust ventilation. The exhaust air must not be recirculated into the house or discharged into an attic or crawl space. An HRV complies with all of these requirements as long as it provides either 20 cfm continuous exhaust or is capable of 50 cfm of intermittent exhaust.
Posted Wed, 02/29/2012 - 08:44