Helpful? 0

Chimney liner needed when converting from tank to tankless water heater?

I am planning to have a tankless water heater installed (not looking for full payback just want continuous water, more floor space, and less natural gas consumption).

I had a couple mechanical contractors come out today to give bids. One mentioned that if I convert to a tankless water heater that I will need to have the chimney lined for my furnace vent pipe. He stated that since they will be removing the vent in the chimney that is for the current water heater, that the furnace will need a liner now to eliminate condensation.

The other guy that came to give a bid never mentioned anything about a liner.

Do I really need a liner in my chimney because I am getting rid of a tank water heater? Eventually my furnace will need upgraded and the chimney venting will be eliminated all together because of the direct venting in current furnaces. If I don't need to get it lined I'd prefer not to spend the money.

Thanks in advance for the comments.

Asked by Aaron Phillips
Posted Mon, 02/03/2014 - 20:53
Edited Tue, 02/04/2014 - 08:28

Tags:

3 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Sounds like the two appliances are vented together at the moment. The usual problem is that the furnace is replaced first, and the water heater is "orphaned" with a chimney that's too big, so it drafts poorly and may have condensation problems. You're removing the water heater first, and the flue size should be evaluated as to whether or not it's suitable for the furnace alone. I would look at the furnace installation manual to see if that tells you what the requirements are, or contact the manufacturer with a description of the chimney and get their feedback. I like bidder #1 for the fact that he recognized the possible issue.

Is this a brick chimney that starts in the basement, or what?

Answered by David Meiland
Posted Mon, 02/03/2014 - 21:07
Edited Mon, 02/03/2014 - 21:08.

2.
Helpful? 0

Thanks David. Yes this is a brick chimney that originates in the basement area. Not sure I will be able to find the manual. I actually have a furnace guy coming this week to do PM on the furnace so I was going to ask his opinion as well. I was just looking for some other's comments as well. Thanks.

Answered by Aaron Phillips
Posted Mon, 02/03/2014 - 21:21

3.
Helpful? 0

Aaron,
David has give you good advice. For more information on these issues, see When a Flue is Too Big.

Answered by Martin Holladay, GBA Advisor
Posted Tue, 02/04/2014 - 08:31

Other Questions in Mechanicals

In Energy efficiency and durability | Asked by Brett Sichello | Jul 31, 14
In Interior design | Asked by Adam Lawrence | Aug 1, 14
In General questions | Asked by Chuck Jensen | Aug 1, 14
In Mechanicals | Asked by Brian Gray | Jul 31, 14
In Green building techniques | Asked by Eric Stear | Jul 31, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!