I have been asked to finish an indoor pool that was built about 18 years ago. The building has stood up well and the only signs of damage were from water intrusion at an exterior door. The building was not heated and the pool was not heated during this time with exhaust only venting, which is why I believe there has been no notable moisture damage.
The renovated room and pool will be heated with a Geo thermal system designed for the room and the humidity. The room is attached to the existing home. 2 inches of spray foam have been applied to all adjoining walls, all doors to the room are exterior insulated doors. The windows and doors are all new and double payne insulated. The GEO system will blow on all doors and windows in addition to the room in general and will included an exhaust only fan to promote negative pressure in the building.
.
Currently the walls are 2x6 @ 16 oc, uninsulated with continuous plywood exterior sheeting, Typar rain screen and vinyl siding.
The roof is a gramble design and about 18 to 20 feet at the center, with plywood decking and 15 lb felt with 30 year shingles.

After reading every post on this site that mentions a pool I understand the consensus is that it is folly to even undertake this project. I have also gleaned the best insulation and vapor barrier design may be the following:

Dense pack the stud bays with cellulose
Cover with 2 inches of foam panels sealed at all joints and at all fasteners.
1/2 inch Dens Armor Plus
Tile with in the first 24 inches of the floor
High quality paint sealer
Treat the ceiling the same as the walls only thicker
Spray the walls adjoining the house to full 5.5 inch depth.

I am in Zone 4A and with in 20 miles of the Atlantic Coast.

If this is not the best wall please recommend a better approach.
What other details should I consider.

Exterior Photo1.56 MB
Asked by Allen Loree
Posted Jun 13, 2012 11:37 PM ET

Tags:

4 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Allen,
I'm a little confused. You wrote that "Currently the walls are 2x6 @ 16 oc, uninsulated," and also that "2 inches of spray foam have been applied to all adjoining walls."

So, how many of the walls are insulated?

I certainly wouldn't insulate a swimming pool room with cellulose. If I had to choose an insulation to install between the studs, I would stick with closed-cell spray polyurethane foam.

The best type of insulation for a swimming pool room is PERSIST insulation -- with all of the insulation on the outside of the structure.

Because the rate of wall and roof problems with swimming pool rooms is so high, I always advise builders involved with such projects to hire a consultant -- ideally, someone from the Building Science Corporation. The cost of the consulting will be much less that the cost of repairing any future moisture problem.

Answered by Martin Holladay
Posted Jun 14, 2012 5:21 AM ET

2.

Touching the exterior is not an option I will be given. Would you add the foam board over the spray in to minimize the thermal bridging at the studs?
I have attached a diagram of the house attachment.

Pool and House Wall.JPG
Answered by Allen Loree
Posted Jun 14, 2012 7:06 AM ET

3.

Im open to a proposal from Building Sicence for consulting as well

Answered by Allen Loree
Posted Jun 14, 2012 7:08 AM ET
Edited Jun 14, 2012 7:09 AM ET.

4.
Answered by Armando Cobo
Posted Jun 14, 2012 8:46 AM ET

Other Questions in Plans Review

Has anyone used Airfoil electrical boxes in Ontario, Canada?

In Building Code Questions | Asked by User-7049195 | Apr 25, 18

Cold pantry in a Passive House via hot water heat pump air exhaust

In General questions | Asked by Mike AbiEzzi | Apr 25, 18

Estimating usage for PV system and choosing panels

In General questions | Asked by User-6952755 | Apr 25, 18

Vented and unvented ceiling, Zip System, metal roofing, underlayment question

In Energy efficiency and durability | Asked by Bridget Lamberson | Jan 10, 17

Recommended European Tilt Turn Options with Thinnest Site Line

In Green products and materials | Asked by J M | Apr 7, 18
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!