GBA Logo horizontal Facebook LinkedIn Email Pinterest Twitter Instagram YouTube Icon Navigation Search Icon Main Search Icon Video Play Icon Audio Play Icon Headphones Icon Plus Icon Minus Icon Check Icon Print Icon Picture icon Single Arrow Icon Double Arrow Icon Hamburger Icon TV Icon Close Icon Sorted Hamburger/Search Icon

Community and Q&A

Cathedral ceiling insulation for a summer cabin

ericski | Posted in Green Building Techniques on

Need help with weekend summer cabin roof insulation, and best way to avoid moisture problems – zone 4, non vented roof.
Metal roof over plywood over 2×4 rafters, then plan to install exterior siding on interior for finished walls.
I currently have extra 2″ rigid insulation sheets that are R10.

Option 1: Cut and cobble rigid insulation against bottom side of roof sheathing, rigid held in place with spray foam. (1A add radiant barrier paint to interior wall panels which will be exterior siding)
Option 2 : Install rigid foam flush with interior rafters leaving 1.5″ airspace between roof sheathing and insulation. Roof is not vented, there are no soffit or ridge vents. (2A would be paint radiant barrier on interior side of roof sheeting)
Option 3: Install batt fiberglass insulation 3.5″ thick with VB on interior side.
Option 4: Install spray foam – lost of $.
Option 5: ?

Summer cabin primary use with AC.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. User avatar GBA Editor
    Martin Holladay | | #1

    Eric,
    Of course it's always better to plan your insulation details before the roofing is on -- because now your options are limited.

    If you can't vent the roof, and you can't install continuous rigid insulation above the roof sheathing, your only choice is closed-cell spray foam on the underside of the roof sheathing.

    If you can retrofit soffit vents and a ridge vent, you'll have more options.

    The cut-and-cobble approach is unsafe for unvented roof assemblies -- it is associated with failures and rot.

    More information in these two articles:

    "How to Build an Insulated Cathedral Ceiling"

    "Cut-and-Cobble Insulation"

  2. Jon R | | #2

    With your limited use, I expect that you would get away with option 1. Three continuous air barriers (the sheathing, the sealed edge foam and something under the rafters) would help (air movement is by far the primary mover of moisture).

    In the unlikely event the air sealing isn't enough, you can control air movement with building pressure (not very expensive for a well sealed building with limited use).

  3. User avatar GBA Editor
    Martin Holladay | | #3

    Eric and Jon,
    There are two problems with Jon's suggestion.

    The first problem is that in most parts of the country, you have to follow the building code -- and according to the usual interpretation of most building inspectors, cut-and-cobble insulation isn't allowed for unvented roof assemblies.

    Of course, Eric may be building in an area that isn't subject to building codes.

    The second problem is than any insulation strategy that depends on "limited use" of the building to avoid moisture problems is risky. Buildings last a long time, and a building that is used occasionally in 2019 might become a full-time home in 2030. That's why our insulation strategies need to be robust.