building-scienceheader image
Are solar-powered attic ventilators green?
Posted on Feb 26 by Peter Yost
Fans that pull hot air out of attics can cause more problems than they solve
At face value, attic exhaust fans make a lot of sense: if your attic is too hot, you force more air through it to cool it down. To be efficient, you use a solar-powered attic exhaust fan. When the sun is shining and heating up your attic, that’s when the photovoltaic(PV) Generation of electricity directly from sunlight. A photovoltaic cell has no moving parts; electrons are energized by sunlight and result in current flow. panel wired to the exhaust fan powers the fan. Pretty slick.
But there is a catch: why is your attic “too hot?” It is probably because living space under the attic is uncomfortable…from the less-than-well insulated and air sealed ceiling that separates the attic from those rooms. If you don’t have a continuous air seal at the ceiling plane, then your solar-powered attic exhaust fan can pull conditioned air into the attic—now that will cool it down! It can be worse than that: if that attic fan is depressurizing living space that has atmospherically-vented gas appliances or a problem with radonColorless, odorless, short-lived radioactive gas that can seep into homes and result in lung cancer risk. Radon and its decay products emit cancer-causing alpha, beta, and gamma particles., you may have moved from wasting energy to indoor air quality problems.
Field research supports these scenarios. Work done in 1995 by John Tooley and Bruce Davis of Advanced Energy Corp (as reported in Home Energy, “Drawbacks of Powered Attic Ventilators”) revealed depressurizationSituation that occurs within a house when the indoor air pressure is lower than that outdoors. Exhaust fans, including bath and kitchen fans, or a clothes dryer can cause depressurization, and it may in turn cause back drafting as well as increased levels of radon within the home. issues and associated energy, moisture and combustion safety problems. And field research done by the Florida Solar Energy Center (FSEC) specifically on solar-powered attic ventilation (“Performance Assessment of Photovoltaic Attic Ventilator Fans”) concluded that the approximately $850 installed cost of the system yielded relatively modest cooling energy savings and an unfavorable payback over more than twenty years.
The bottom line? Proceed with caution. If you have a well-sealed and insulated attic floor and either no HVAC(Heating, ventilation, and air conditioning). Collectively, the mechanical systems that heat, ventilate, and cool a building. equipment in the attic or all of the HVAC equipment and ducts in the attic are well sealed, then you could install solar-powered attic ventilation with some cooling energy benefit and little potential for safety or indoor air quality problems. For far too many homes, this is a mighty big “if.”
Joe Lstiburek of Building Science Corp. puts it this way:
“In order for the fan to work the air needs to come from the outside and not be pulled from the house so this means that the attic ceiling needs to be airtight. If the attic ceiling is airtight you don’t need the fan. Your money is better spent on something else.”
For most homes, it will be “greener” to take the money you would have spent on the PVPhotovoltaics. Generation of electricity directly from sunlight. A photovoltaic (PV) cell has no moving parts; electrons are energized by sunlight and result in current flow.-powered attic ventilation and upgrade the air sealing and insulation in your attic and on your HVAC system.
Tags: , , , , , , , , , , ,
Image Credits:
  1. Florida Solar Energy Center
Jul 18, 2009
10:47 AM EDT
Solar attic fan and radiation
by solar fan
Why is the attic too hot? Not because of heat from below, but because of solar heating of the uninsulated roof! Too bad none of the authors are physicists. They seem to discount the fact that heat travels by radiation as well as by convection. An attic is heated to a very high temperature by solar heating. This high temperature will result in heat radiation from the attic into the home below. Ventilators cool the attic convectively so that the temperature is lower and the heat transfer into the home by radiation is much lower.
Jul 19, 2009
4:21 AM EDT
Dear Solar Fan,
I'm not a physicist, but I know that powered attic ventilators cause more problems than they solve. I'm well aware that the sun can make some attics quite hot. Here's the basic solution: Be sure your ceiling is carefully air sealed, and include enough insulation to provide thermal separation between your living space and your attic.
If your hot attic is making you uncomfortable during the summer, I guarantee that either (a) someone forgot to include an adequate air barrier at the ceiling plane, or — more likely — (b) the attic floor is inadequately insulated.
I've said it before, and I'll say it again: as long as you keep HVAC equipment and ductwork out of your attic, it really doesn't matter how hot your attic gets.
Depressurizing your attic with an attic fan is asking for trouble. In most homes, a powered attic ventilator will suck conditioned air from your home, raising your energy bills.
Jul 20, 2009
5:31 AM EDT
On not being a physicist
by Peter Yost
Actually, the quote near the end of the article is from a physicist. We know our thermodynamics a bit. It's not that these fans are universally a bad idea; it's just that too often they are used without a thorough understanding of building physics.
Jul 31, 2009
1:07 AM EDT
Solar Energy
by John
Broan Solar Powered Attic Ventilators operate without fuel, waste or pollution. And because they are a totally solar-powered solution, they can count as points towards Green building. All NGOs trying to make this world green should involve in educating people to utilize products like this.
Here also we can check the updates of solar energy,
http://www.BuildEnergy.org
Aug 2, 2009
11:23 PM EDT
Attic Fans
by H. Kaplan, M.S. P.E. LEED AP
Actually you are all right. Air takes the path of least resistance. Which means, unless there is an intake into the attic (e.g. a louver) that is sufficiently large enough (static pressure say less than 0.05"w.g.) then the attic could become negative enough to draw air from the house. And yes it is it is good to run air through the attic that will come from the outside to lower the temperature in the attic. The temp. difference (delta T) between the inside of the house and the attic will then be less, therefore less heat transfer from conduction. Increasing the insulation would be helpful also as this is part of the heat transfer equation (q=UxAxdelta T)where U is 1 over the insulation R value). For those in a high humid area a vapor barrier on the warm side is highly suggested. Don't place another vapor barrier on top of your attic floor insulation. Hope this helps. Regards.
Aug 3, 2009
9:34 PM EDT
Positive pressure?
by William Clarke
I am not a physisist, but I would like a cooler attic, less because of heat transfer to the living space, than because I store stuff up there! I'm glad to know about the dangers of sucking air up from the living space (although no AC, so maybe not a big deal). What about drawing outside air in with a fan at one of the gable vents? Obviously you don't want to push heated air into the living space, but wouldn't a ridge vent and the 2nd gable vent, couple with a reasonably tight and well insulated ceiling, make that unlikely? I've also considered stapleing relective insulation to the rafters, but leaving it open at the top and bottom, to reduce radiant heat gain. Would that be pointless? Thanks!
Aug 4, 2009
8:54 AM EDT
THings to do besides fans to cool attics in hot climates
by Peter Yost
Any fan in the attic can pull air from the conditioned space, depending on the quality and continuity of the air barrier at the ceiling plane. If you knew that you had a good air barrier then pv-powered attic exhaust fans work. BUt without a good air barrier, you just don't know.
A radiant barrier on the underside of the rafters is a good idea in a hot climate. Remember that in order for any radiant barrier to work it must face an air space and it must stay clean (since radiation and emissivity are surface properties).
Sep 24, 2009
11:44 AM EDT
Solar Attic Fans
by Travis Hipp
I find this to be a very misleading article. Begin both an engineer and attic ventilation expert, I think you owe it to your readers to present a non-biased treatment of the topic. While solar attic fans are not the “magic bullet” for every situation, the technology in general is both soundly based in physics and does offer real benefits for many applications. The key for success is in the proper installation and application of the product.
You reference a couple of articles as the basis of your claims (actually the same two articles that are always referenced). The first article by Advanced Energy talks about the potential for attic depressurization and is actually a good study on what can happen if you improperly install an AC powered fan. However if proper installation guidelines are followed and the installer allows for the proper amount of intake ventilation to support the fan, attic depressurization is both unlikely and improbable. Air flow will always follow the path of least resistance, so just allow for enough attic air intake ventilation and there is no issue. Also, most solar attic fans are designed in such a way that they cannot put up much pressure head. In layman terms, this means that a given solar attic fan is far less likely to present a negative pressure problem than the similar AC powered attic fans discussed in the study.
The second article you referenced was the Florida study on solar attic fan economics. The study found that the solar attic fan only saved an average 6% electrical usage on the home. However if you read the study, you’ll find that the home they used not only had an attic radiant barrier installed (this blocks on average at least 50% of attic heat gain), but also the home did not have HVAC equipment installed in the attic. Even with the radiant barrier installed, the solar attic fan still dropped the attic temperature over 20F and in the words of the home owner “made the house feel more comfortable”. Also for noting, the study assumed an installed cost of $850 and did not account for any rebates or tax incentives when they calculated the potential savings. Bottom line, a home without an existing radiant barrier would realize at least twice the savings (12%) of the case study home and potentially much more if their HVAC equipment is located in the attic (which is the situation for millions of homes in the south and southwest). Throw in the existing tax incentives of solar attic fans, and what you find is a completely different picture than what was presented.
Instead of assuming that solar attic fans will cause problems, why not educate the pubic on how to properly install them? This is simply another tool that can be used to reduce energy consumption and when compared to alternative methods of reducing attic temperature, the economics actually favor solar attic fans.
Sep 24, 2009
12:13 PM EDT
This article is misleading
by Peter Yost
Hi Travis - thanks for your comments and perspective. You made me go back and re-read what I had written. Sorry, but I don't think it is misleading, inaccurate, or biased. I did not say don't use solar-powered attic exhaust fans, but to "proceed with caution." And I did say to carefully compare this investment to improvements to the building envelope.
If I could be convinced that everyone understood building physics as well as you do, and that the installer of the PV-powered attic exhaust system ensured that there was no potential for depressurizing living space, I would be more generally supportive of the technology's use. But some manufacturers of these systems do not even mention the issue of air sealing the ceiling plane or depressurization potential. That is my concern and why I would like GBA folks to understand the issues as they consider this technology.
Oct 2, 2009
12:35 PM EDT
Path of Least Resistance
by Stephen Colley
Attic airflow is another consideration to be considered. Improperly placed, an attic exhaust fan (PV or AC) could suck air from an adjacent ridge vent or gable vent and not be as effective as desired in removing hot air from remote areas in the attic. We depend so much on soffit vents, but it doesn't take long for these to become blocked by dust, cobwebs, and other attic "schmutz" seriously lessening their designed effectiveness. Great discussion, folks.
Oct 6, 2009
12:06 PM EDT
Hot air !
by Steven Leighton
Dear Mr Yost,
I can't argue with "Fans that pull hot air out of attics can cause more problems than they solve" but you didn't do a good enough job of defining the "can".Perhaps you ought to have swapped "can" for "might" and we would have all been happier.
Still, you generated great input from the people commenting above ... so overall a good job.
Oct 31, 2009
3:59 AM EDT
Solar Powered Attic Fan
by Anonymous
Some of the problems that are envisioned by these so called "experts" are laughable, but could possiby occur in rare, isolated cases. If your attic has properly sized and properly installed ventilation openings, then an exhaust fan will do quite well in pulling out the air heated up by the solar radiation hitting the roof. The attic space will be much cooler throughout the day, putting less load on the living space AC system. If the AC system ducting runs through the attic and leaks to the extent that a ventilation fan will pull a significant amount of the AC air from the living space, the attic is probably being cooled by so much leakage and doesn't get warm. This is a loss of efficiency in the home AC system. But if the attic gets hot and remains hot throughout the day and evening, a solar powered fan is just the ticket. It will keep the attic much cooler throughout the day and cool off the attic with the late afternoon, early evening lower air temperature. This reduces the load on the AC system by reducing the amount of heat that radiates from the attic into the living space. Even if your attic is insulated well, a significant amount of heat from the hot air in the attic will still enter the living space. Being able to lower signigicantly the attic temperature, without any expenditure for the power required to drive the ventilation fan, is a good idea and will save you money.
Post new comment
The content of this field is kept private and will not be shown publicly.
Discussion policy: The editorial staff at GreenBuildingAdvisor.com does review user submissions. Please be respectful of others. Inappropriate content will be removed.
  • Web page addresses and e-mail addresses turn into links automatically.
  • Allowed HTML tags: <a> <em> <strong> <cite> <code> <ul> <ol> <li> <dl> <dt> <dd> <blockquote>
  • Lines and paragraphs break automatically.
* required fields