green-building-newsheader image
0 Helpful?
Irish Passive House Raises Bar for Eco Design
Thick insulation and attention to airtightness help this new home in County Cork meet the Passivhaus standard
Posted on Dec 1 2011 by GBA Team
Reprinted with permission from Construct Ireland magazine.
Sally O’Leary says that when a site became available near the site of an old family home, she couldn’t pass up the opportunity to buy it. She’d been looking for a site to build on with her husband John. “We always wanted energy efficiency, I think nowadays that’s something that people have to do," she says.
The spent a few years trying to get planning permission before turning to Cork-based Wain Morehead Architects. For Sally, it was important their design showed respect for their site — an awkward, sloping patch of land overlooking a local river.
Energy efficiency was important to the O’Learys, but architect John Morehead suggested taking things further and aiming for the more onerous passive houseA residential building construction standard requiring very low levels of air leakage, very high levels of insulation, and windows with a very low U-factor. Developed in the early 1990s by Bo Adamson and Wolfgang Feist, the standard is now promoted by the Passivhaus Institut in Darmstadt, Germany. To meet the standard, a home must have an infiltration rate no greater than 0.60 AC/H @ 50 pascals, a maximum annual heating energy use of 15 kWh per square meter (4,755 Btu per square foot), a maximum annual cooling energy use of 15 kWh per square meter (1.39 kWh per square foot), and maximum source energy use for all purposes of 120 kWh per square meter (11.1 kWh per square foot). The standard recommends, but does not require, a maximum design heating load of 10 W per square meter and windows with a maximum U-factor of 0.14. The Passivhaus standard was developed for buildings in central and northern Europe; efforts are underway to clarify the best techniques to achieve the standard for buildings in hot climates. standard. “Passive was a complete dream,” Sally says.
Building envelope
The couple wanted a timber frame house, but as the design envisaged the house partially nestling into the ground, using timber wasn’t structurally feasible for the lower floor. John Morehead originally planned to use concrete block with external insulation here, but contractor Twomey Construction suggested going with insulated concrete formwork (ICFInsulated concrete form. Hollow insulated forms, usually made from expanded polystyrene (EPS), used for building walls (foundation and above-ground); after stacking and stabilizing the forms, the aligned cores are filled with concrete, which provides the wall structure.) instead.
PROJECT OVERVIEW
Building type: 238 sq. m. (2,562 sq. ft.) detached two-story house
Space heating demand (PHPP): 11kWh/m2/year
Heat load (PHPP): 8W/m2
Ground floor: Raft foundation insulated with 140 mm (5.5 in.) Styrozone insulation and 60 mm (2.4 in.) Kingspan insulation. U-value: 0.115 W/m2K
Ground floor walls: Tegral Natura Pelicolour rainscreenConstruction detail appropriate for all but the driest climates to prevent moisture entry and to extend the life of siding and sheathing materials; most commonly produced by installing thin strapping to hold the siding away from the sheathing by a quarter-inch to three-quarters of an inch. on rendered insulated concrete formwork with 100 mm graphite EPSExpanded polystyrene. Type of rigid foam insulation that, unlike extruded polystyrene (XPS), does not contain ozone-depleting HCFCs. EPS frequently has a high recycled content. Its vapor permeability is higher and its R-value lower than XPS insulation. EPS insulation is classified by type: Type I is lowest in density and strength and Type X is highest. externally, 50mm graphite EPS internally and a 150/200mm concrete core. 100 mm service cavity insulated with Rockwool and 15mm Fermacell internally. U-value: 0.12 W/m2K
First floor walls: Timber frame with 22 mm larch claddingMaterials used on the roof and walls to enclose a house, providing protection against weather. externally, followed inside by 50 x 50 mm treated battens and counter-batten, Tyvek UV facade membrane, 22 mm woodfibre board, 235 x 38 mm cellulose-filled timber stud, 15 mm taped and sealed OSB, 50 mm service cavity insulated with Rockwool insulation, and 15 mm Fermacell board internally. U-value: 0.13 W/m2K
Roof: Tegral fibre cement slates externally on 50x35 battens/counter battens, followed underneath by breathable roofing underlay, 346 mm timber I-joists fully filled with cellulose insulationThermal insulation made from recycled newspaper or other wastepaper; often treated with borates for fire and insect protection., 15 mm taped & sealed OSB, 50 mm uninsulated service cavity, 12.5 mm plasterboard ceiling. U-value: 0.11 W/m2K
Windows: Katzbeck triple-glazed aluminum-clad larch windows, with an overall U-value of 0.82 W/m2K and a g-value of 0.55. Velux skylights – with a frame U-value of 1.5 W/m2K, a glass U-value of 0.5 W/m2K and a g-value of 0.46 – were also installed
Heating system: Patented electrically powered infrared local ceramic heaters, plus three square meters Kingspan Thermomax solar thermal evacuated tubes. Back-up gas boiler for towel rails in bathroom and radiator in laundry room drying tower
Ventilation: Paul Santos 370DC heat-recovery ventilation(HRV). Balanced ventilation system in which most of the heat from outgoing exhaust air is transferred to incoming fresh air via an air-to-air heat exchanger; a similar device, an energy-recovery ventilator, also transfers water vapor. HRVs recover 50% to 80% of the heat in exhausted air. In hot climates, the function is reversed so that the cooler inside air reduces the temperature of the incoming hot air. system — Passivhaus Institut certified to have heat recovery rate of 84% / EN 308 certified efficiency of 92.7%
Airtightness: 0.6 air changes per hour at 50 pascals pressure
Furniture fit-out: Most of the built-in furniture came from Noblessa, a German fitted furniture manufacturer. All timber used by Noblessa comes from PEFC certified sources
PROJECT TEAM
Clients: Sally & John O’Leary
Architects: Wain Morehead Architects Ltd (team: John Morehead, Paul O'Leary, Evan Finnegan)
Contractor: Twomey Construction
Quantity surveyors: Richard Leonard Associates
Civil/structural engineer: Horgan Lynch Consulting Engineers
Services consultants: DW EcoCo
Airtightness tester: Tremora Ltd
Timber frame: Eco Timber Frame
Insulated concrete formwork: Thermohouse
Heat recovery ventilation: Ollie McPhillips Ltd
Windows & doors: West Building Products Ltd
Airtightness products: Ecological Building Systems
Solar thermal system: Kingspan Renewables
Rainwater Harvesting: Ireland Waste Water
Ceramic heaters: Ceramicx Ltd .
Built-in furniture fit out: Classic Kitchens
Skylights: Velux
Thermal breaks: Isokorb by Schöck
Larch siding: Unterluggauer , Austria
Lower level cladding: Tegral Natura Pelicolour by Tegral Building Products
“It’s very accurate,” the company’s Brian Twomey says of ICF. “You can get it very precise.” He’s also drawn by the fact that the structural, insulation and airtightness components of the wall are built in one system by one type of tradesperson.
Killarney-based Thermohouse supplied the ICF system — essentially two vertically-stacked walls of polystyrene block, built up like Lego, with concrete poured between. The walls have a 100 mm (4-inch) service cavity on the inside — this is insulated with Rockwool and lined with Fermacell board, a mixture of gypsum, recycled paper and water.
The ICF system features 100 mm (4 inches) of gray EPS insulation on the outside and 50 mm (2 inches) on the inside, with a 150 mm (6-inch) concrete core sandwiched between. The concrete layer was beefed up to 200 mm (8 inches) for structural support where the wall was built into the ground, and the walls are reinforced with extra steel here too. “We can design ICF buildings to withstand earthquakes of up to 7.2 on the Richter scale, and up to ten stories high,” Thermohouse’s Jack O’Driscoll says.
“It would certainly be a much faster build than a traditional type building,” O’Driscoll says of ICF. Thermohouse frequently uses ground granulated blast-furnace slag — a low carbon “green” cement derived from recycled steel industry waste — for its projects too. The company can deliver ultra low U-values by beefing up the outer layer of EPS, and can supply ICF roofing systems too.
At Carrigaline, the house has a standard raft foundation, and the ground floor features 140 mm (5.5 inches) of Kingspan Styrozone insulation and another 60 mm (2.4 inches) of Kingspan rigid insulation. The first floor was built with a timber frame system manufactured by local firm Eco Timber Frame. The company’s Donal Spillane calls the project a “flagship house” for the company.
The timber frame walls feature 235 mm (9 1/4 inches) of cellulose insulation — essentially recycled newspaper — with a further 50 mm (2 inches) of Rockwool insulation inside the service cavity. Outside, the walls are finished with Austrian larch cladding. The roof boasts 345 mm (13 1/2 inches) of cellulose insulation, and is finished externally with Tegral fiber-cement slates.
Eco Timber Frame – who previously worked with Cyril Mannion of Passive House Builders on a certified passive house in Athenry – say they can deliver U-values as good as 0.09 W/m2K with their system. “It’s always a balance between cost and extremely low U-values,” says Donal Spillane. “Once it’s below 0.15 W/m2K, that’s adequate for most situations.”
Climatic concerns
While designing the house, architect John Morehead started examining the Irish climate data in the Passive House Planning Package, the software used to design passive houses. PHPP offers two default Irish climate data sets — one for Dublin and one for Birr.
But Morehead found flaws in the figures for Dublin. “There was too much solar radiation and temperatures were too high in January. It was effectively indicating that it was much milder and sunnier than it is,” he says. Someone designing a house with such data could inadvertently underestimate the energy needed to keep it comfortable and under-specify the heating system.
Ireland is a small island with a big coastline and varied topography, so our climate varies a lot from place to place — Morehead says this makes it particularly important to use site-specific rather than generic climate data. Wain Morehead Architecture now produce location-specific data using a methodology suitable for use in low energy and passive house buildings, taking into account data from local weather stations, satellite data and local topography — all processed with specialist software.
Using site-specific climate data for the Carrigaline passive house — in the sunny south west — allowed Morehead to design the house with a lot more glazingWhen referring to windows or doors, the transparent or translucent layer that transmits light. High-performance glazing may include multiple layers of glass or plastic, low-e coatings, and low-conductivity gas fill. than you might expect possible.
Morehead says if he’d used data from Birr or Dublin and built the house with more insulation and smaller windows, it might have hit the passive house standard but been less comfortable to live in. “It’s all about achieving a balance,” he says. He adds that choosing windows that let through as much solar radiation as possible — measured in a figure known as g-value — is crucial. “I believe on the south side it’s even more critical than the U-value of the glass,” he says.
He specified Katzbeck triple-glazed aluminium-clad larch windows for the project, supplied by Cork-based West Building Products. The windows have an overall U-value of 0.82 W/m2K, and a g-value of 0.55 – the scale for g-values goes from zero to one, with higher figures meaning greater solar gains. Morehead says the glazing specified reduced the house’s heat load by 2KW compared to using windows with a g-value of 0.52.
Airtight challenge
An airtightness test at the house produced a result just under the required passive house standard of 0.6 air changes per hour under pressure test conditions of 50 pascals. “We’ve got a lot of folding doors and things which are pushing things to the limit,” Morehead says. “We hit the target, we were very relieved.”
On the ground floor, the external render [stucco] acts as the airtightness layer — this ensures continuity with the windows, which do not physically connect to the concrete wall element in ICF. The OSB board serves as the airtightness layer in the timber frame upstairs, and is joined to the render downstairs by an airtight membrane. “We had to be very considerate of the junctions before we even started building,” contractor Brian Twomey says.
"Airtightness was a major issue," adds John Kiely, electrician on the project. He says building airtight meant all electrical runs had to be planned in detail with the architect and contractor before work started. "It obviously took longer than usual, but paying attention to detail was very important. I would have made all my staff aware of airtightness and how important it was."
John Morehead adds: “There's quite a busy road across the river, and you can't hear a squeak. I think it's a lot to do with the airtightness achieved. It’s absolutely silent in there.”
He attributes the struggle to get to the passive airtightness standard to the complex shape and articulation of the house. A large folding wall on the first floor divides the main living space from the porch outside. “Quite a substantial area of the accommodation can be opened up to the elements outside the heating season, taking account of the fact that the principal accommodation is located on the upper floor level. The deep roof overhangs and balcony actively prevent overheating in summer,” he says.
The design of the house was “heavily influenced by the fact we were on a water frontage”, he adds — for a start, the living spaces are upstairs while bedrooms are downstairs. “We wanted to maximize the views down to the river and facilitate and encourage family activity, inside and out, on the upper level.”
Patented heating design
Morehead took an unconventional approach when deciding how to heat the house — he designed a unique infrared [electric resistance] heating system that he’s since patented. “We’ve got localized infrared emitters using ceramic elements manufactured in west Cork,” he explains. He says infrared radiation has a wavelength that’s easily absorbed by the skin, meaning it can heat the occupants of the house easily at a lower temperature than is usually required. The house should be run at 18C – in contrast 20C or 22C might be typical in a conventionally heated house.
Morehead says that because it only generates a wavelength that is “useful”, it’s extremely efficient. “It heats the person but not the air, permitting the ambient temperature to be maintained throughout the dwelling.”
The system can be activated individually in selected rooms, allowing the O’Learys to maintain comfort as required on a room-by-room basis. Powered by mains electricity, it’s also integrated with the house's heat recovery ventilation system. Sally was happy to be a guinea pig for the infrared system. “[John Morehead] lent me a prototype that I put in the kitchen and I didn’t want to give it back,” she laughs. “If he could design one for every woman’s handbag he’d be the richest man in the country.”
Three square meters (32.3 sq. ft.) of Kingspan Thermomax solar thermal collectors help provide hot water, and a Paul Santos 370 DC heat-recovery ventilation system supplied by Ollie McPhilips Ltd features too. The unit is certified by the Passivhaus Institut to deliver a heat recovery rate of 84%, and achieves 92.7 % efficiency according to the EN 308 testing standard. The Santos unit was installed along with Paul Octopus Easy Flex flexible ducting.
The O’Learys moved in to the house in April. “At the moment we’re running at a comfortable 20 degrees of temperature constantly, and that’s without heating,” Sally told Construct Ireland in June. “We’re looking forward to minus ten this year! We don’t have any worries.” She jokes that when it does get cold they can “always do something mad like turn on a towel rail.”
Contractor Brian Twomey says the house presented a combination of challenges — a tricky structure, a unique design and the need to hit the passive standard. “It's easy to do one but trying to do all just made it that bit more complicated. Every time you consider a junction you have to consider the thermal bridgingHeat flow that occurs across more conductive components in an otherwise well-insulated material, resulting in disproportionately significant heat loss. For example, steel studs in an insulated wall dramatically reduce the overall energy performance of the wall, because of thermal bridging through the steel. , the structure, the airtightness and then you've got to consider the aesthetics."
The team analyzed the house using thermography to look for cold bridging during the cold snap in January. “We did a lot of work there with the camera during the cold spell and it was remarkable the lack of cold bridging. Obviously the client hasn't been through a full winter, but we found at the depths of winter...you had guys working inside in their t-shirts,” Twomey says.
John Morehead says working with a trusting client and a great team made a potentially awkward build much easier. “It was a joy to work on, which can be rare for such a complex project,” he says.
"Everyone involved was locally based, and that was really nice,” he adds. “Everyone knew each other and they were all very interested in achieving the passive house standard."
He says the house is proof that a “reasonable standard” low energy design can go passive without major modifications — and without sacrificing good design. “It doesn’t have to look like something designed by a physicist," he says.
Tags: , , , , , , , , , ,
Image Credits:
  1. All photos: Construct Ireland
1.
Dec 1, 2011 8:12 AM ET
Nice project.
by James Morgan
0 Helpful?
Service cavity in the walls and ceilings is a nice touch. I'm surprised that the sliding folding door to the porch didn't blow the air leakage test - must be a better product than those I've seen around here. I'd be concerned about gasket durability in the long term though. 'Timber frame' might be misleading for N. American readers - I think here it's the same as the UK usage simply meaning dimension lumber stud framing.