How do you reconcile continuous insulation requirements with rated assembly requirements?

The application is multifamily construction. We have energy requirements stipulating continuous R-3 insulation, in addition to required cavity insulation. We also have rated exterior wall assembly requirements.

I have not found any UL or GA assemblies that work, nor have I found any SIS product that has been UL tested.

Asked by david nofsinger
Posted Tue, 11/27/2012 - 10:59
Edited Tue, 11/27/2012 - 12:02

Tags:

4 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Half inch fire-rated rigid polyiso, mayhaps? What UL test does it need to meet?

Answered by Dana Dorsett
Posted Tue, 11/27/2012 - 16:02

2.
Helpful? 0

U356 and/or U305

Answered by david nofsinger
Posted Tue, 11/27/2012 - 17:22

3.
Helpful? 0

UL U356 SIS test reports:

http://sbcri.info/docs/pa/dow/TER_1109_01ULU356_Summary_Fire_Endurance_A...

http://sbcri.info/docs/pa/dow/TER_1109_01_Dow_SIS_Fire_Endurance_Assembl...

I'd be surprised if 1.25" Roxul Comfortboard over OSB or ply wouldn't pass the test, but I didn't find U305 or U356 in a cursory scan. http://www.roxul.com/residential/products/roxul+comfortboard+is

Answered by Dana Dorsett
Posted Tue, 11/27/2012 - 17:56

4.
Helpful? 0

Thanks for the help!

Answered by david nofsinger
Posted Tue, 11/27/2012 - 18:01

Other Questions in Building Code Questions

In Mechanicals | Asked by Kevin Wyckoff | Apr 23, 14
In Green products and materials | Asked by Martin Holladay | Apr 24, 14
In Energy efficiency and durability | Asked by John Brooks | Apr 8, 14
In Energy efficiency and durability | Asked by Hugh Stearns | Apr 24, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!