In a warm climate, what are the advantages and disadvantages of spray foam versus radiant barrier in attics?

What works best and why?

Asked by Anonymous
Posted May 6, 2010 10:22 AM ET
Edited May 6, 2010 12:41 PM ET

Tags:

3 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Brad,
Briefly, the answer is spray foam.

But honestly, you need to provide more information.

1. Where do you intend to install these products? Under the roof sheathing or on the attic floor?

2. Is there any ductwork in the attic?

3. Is the air handler located in the attic?

4. What problem are you trying to address?

Answered by Martin Holladay
Posted May 6, 2010 12:42 PM ET

2.

Brad...is you location warm-dry or warm-humid?

I wish the GBA would add "Job Location or Climate Zone" as a "required field" with every question!!!

Answered by Armando Cobo
Posted May 6, 2010 12:53 PM ET

3.

Assuming you are in a hot climate, the answer in order of preference:

a well insulated ceiling using blown insulation and the ducts and air handler inside the conditioned space

a well insulated ceiling using blown insulation and very tight and well insulated ducts in the attic with an option to go for either a cool roof or a radiant barrier on the roof line if they are not expsnive -- the extra cooling savings might be about 0.1 kWh per square foot

I don't really see the scenario where the foam roof makes much sense unless you want a conditioned attic for other reasons. It's just too expensive given the other options to reduce cooling loads associated with attic and ducts

Answered by Michael Blasnik
Posted May 6, 2010 1:50 PM ET

Other Questions in Energy efficiency and durability

How to deal with duct-work that installed in unconditioned attic and a powered attic ventilator?

In Energy efficiency and durability | Asked by TedLiu | May 22, 17

Calculating Annual heating losses

In Energy efficiency and durability | Asked by davor radman | May 24, 17

Heat loss calculation for a ductless system

In Energy efficiency and durability | Asked by John Brown | May 24, 17

Dense packing cellulose with the Krendl 425

In Energy efficiency and durability | Asked by Joe Duchek | May 23, 17

Average lighting, appliance and plug loads for PV sizing?

In Mechanicals | Asked by Burke Stoller | May 23, 17
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!