Helpful? 0

Floating plywood floor on rigid foam insulation on concrete?

I am proposing a project for a slab on grade Habitat house with 2" of foam under the slab and 1 1/2" or 2" of foam on top of the slab with 3/4" t&g plywood or osb floor. I want to float the plywood rather than use screeds to minimize thermal bridges. The interior walls are all non-bearing so they can be fastened to the plywood. I am certain that this is not an original idea so I would like to know if anyone has tried this and what the down side issues might be.

Habitat.pdf34.17 KB
Asked by Philip Koepf
Posted Wed, 12/14/2011 - 09:36
Edited Wed, 12/14/2011 - 11:17

Tags:

11 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Philip,
1. Why not put all of the rigid foam under the slab instead of putting some of it on top?

2. If you really want to put some of your rigid foam on top of your slab, here are some links to show you how other people have been doing it:

Fine Homebuilding: The Stay-Dry, No-Mold Finished Basement

Fine Homebuilding Q&A: Finishing a basement floor

GBA Q&A: Basement floor insulation retrofit

Answered by Martin Holladay, GBA Advisor
Posted Wed, 12/14/2011 - 10:43
Edited Wed, 12/14/2011 - 11:16.

2.
Helpful? 0

Thanks. I guess the short answer for the concrete sandwich is that it is more comfortable for the occupants to stand on a wood floor rather than concrete. Just that little bit of give in the material seems to make a difference. I have no specific data on that just my opinion. Thanks for the links. I read though them and I think the trick is to have some way to tie the pieces together.

Answered by Philip Koepf
Posted Wed, 12/14/2011 - 11:20

3.
Helpful? 0

I definitely agree with Martin--putting all the foam under the slab is preferable and a lot less work. Some friends and I recently worked on their basement, where we did an assembly along these lines--no existing basement slab insulation. The original design intent was 1" XPS with taped seams, polyethylene, 3/4" T&G plywood "floating" above it. However, we found that the plywood curled or "potato chipped" too much, and we had to fasten it down to the concrete with Tapcons, about 6 per 4x8 sheet. Note that Tapcons won't self-countersink--you need to drill a countersink in order to get them flush. Perhaps you could do it with two layers of 3/4" or 1/2" plywood, but at that point, you're getting into a pretty ridiculous amount of material to lay down just for a bit of cushion.

As an FYI, our recommendation for an ideal slab can be found at these web pages:

http://www.buildingscience.com/documents/insights/bsi-001-the-perfect-wall
http://www.buildingscience.com/documents/insights/bsi-003-concrete-floor...

IMG01223.jpg
Answered by Kohta Ueno
Posted Wed, 12/14/2011 - 11:49

4.
Helpful? 0

Thanks again. I was hoping that someone had installed this system before without issues but I suspected that the potato chip effect might be a problem. I don't want to go there. I think I will explore the foam fastened down with screeds and then plywood or maybe just put all the foam under the slab. The other issues with the concrete slab on top is the sheet vinyl they typically use in the kitchens and baths. The low VOC adhesives just won't work on new concrete without much fussing around.

Answered by Philip Koepf
Posted Wed, 12/14/2011 - 12:30

5.
Helpful? 0

You might also try two layers of 7/16 OSB with staggered joints both directions (glued and screwed).
Less likely to curl and no more expensive than 3/4' T&G.

Answered by Richard Patterman
Posted Wed, 12/14/2011 - 13:00

6.
Helpful? 0

Thanks again.

Answered by Philip Koepf
Posted Wed, 12/14/2011 - 13:10

7.
Helpful? 0

There is a flooring product that is an adhesive and vapor barrier that I don't have the name of at my fingertips, bucket is in the garage.

I used that and then discovered a wonderful tool called a "T nailer"

Air powered concrete nailer, works great but you must have the right length nails as they don't drive more than 1/2 inch or so. Fussier than a framing nailer, but you can drive 20 nails a minute instead of 20 an hour for tapcons. Great for this application where you are really just holding while the glue dries and in case it fails. Absolutely love the thing

Insulate under tho....

Answered by Keith Gustafson
Posted Wed, 12/14/2011 - 13:11
Edited Wed, 12/14/2011 - 13:12.

8.
Helpful? 0

I think the product was 'Dritac 1001' but will double check

[edit 12/16] that is in fact the stuff, seems to work great

Answered by Keith Gustafson
Posted Wed, 12/14/2011 - 13:19
Edited Fri, 12/16/2011 - 16:39.

9.
Helpful? 0

I did exactly what Richard P suggested, 11 years ago in our basement bedroom. Were I to do it again, I'd use plywood instead of OSB. No issues have as yet surfaced.

Answered by John Klingel
Posted Wed, 12/14/2011 - 14:46

10.
Helpful? 0

This is awesome. The first time I have ever submitted a question to a blog and you all have been hugely helpful. Hope to return the favor at some time. Philip

Answered by Philip Koepf
Posted Wed, 12/14/2011 - 15:19

11.
Helpful? 0

Personally I'd place the insulation underneath to maintain the thermal mass. Then just squeeze out a thick bead of PL glue 12" on center. That will eliminate the unforgiving concrete and save a bundle. Finish the underside of plywood with shellac.

Answered by Dave Cummings
Posted Wed, 12/14/2011 - 21:24

Other Questions in GBA Pro help

In Building Code Questions | Asked by michael maines | May 23, 12
In Energy efficiency and durability | Asked by Victor Burgos | May 23, 12
In Energy efficiency and durability | Asked by David Slade | May 21, 12
In General questions | Asked by Robert Hronek | May 23, 12
In General questions | Asked by Holger Herrmann | May 23, 12
Register for a free account and join the conversation