Can Open-Cell Foam Waste be Used as Attic Insulation?
A homeowner looks for a way to dispose of post-installation waste
The other side of foam. Open-cell foam insulation has several advantages, but disposal of installation waste and the chemical composition of fire retardants are among the negatives.
UPDATED 1/19/11 with comments from Peter Yost
Open-cell polyurethane foam expands dramatically as soon as it hits its target, rapidly filling wall cavities and typically mushrooming beyond the stud line. After it's firmed up, installers trim away the excess so drywall or other wall finishes can be put up.
The installer who sprayed open-cell foam into the exterior walls of Peter Halkias' house has packed up his truck and hit the road, leaving him with “bags and bags” of excess foam. Halkias knew up front that disposal would be his problem. Now he wonders what to do with it, and whether it can be broken up into finer chunks and spread over the fiberglass batt insulationInsulation, usually of fiberglass or mineral wool and often faced with paper, typically installed between studs in walls and between joists in ceiling cavities. Correct installation is crucial to performance. already in his attic.
“Are there any code violations involved in doing this?” he asks in a Q&A post. “The only thing I can think of is an issue of flammability. The attic is fully vented and any light fixtures located in the ceiling joist bays are rated IC and airtight. I am trying to kill two birds with one stone: Get rid of the waste and add some insulation R-valueMeasure of resistance to heat flow; the higher the R-value, the lower the heat loss. The inverse of U-factor. to my attic ceiling.”
The replies to Halkias' post, the subject of this week's Q&A Spotlight, touch not only on the merits of his plan but also the knotty disposal issue in general. And like a concurrent thread elsewhere on the site, it's an opening to discuss the potential downsides to spray-foam insulation.
First, will it work?
GBAGreenBuildingAdvisor.com senior editor Martin Holladay doubts much will be gained by Halkias' plan. First, exposed foam is a fire hazard, Holladay said, and used in this way it won't offer much in the way of insulation: “Unlike undisturbed foam that is sprayed in place, broken pieces of cured foam provide no resistance to air flow,” he wrote. “I doubt whether they provide much R-value, since air can easily pass through the broken pieces of foam.”
RELATED ARTICLES
Spray Foam Insulation: Open and Closed Cell
Does Spray Foam Insulation Out-Gas Poisonous Fumes?
Open-Cell Foam Beats Closed-Cell Foam
GREEN PRODUCT GUIDE
However, Bill Clark disputed Holladay's advice. According to Clark, many spray foams are approved for use in attics without any fire coating. As to the insulation value of the offcuts, Clark said, “Excess cut-off spray foam insulation will generally NOT allow air to pass through it, and even if it does, all traditionally used insulation products except spray foam allow air to move through them.”
John Klingel wondered whether the pieces of excess foam could be pitched into the hopper with cellulose and blown in over the fiberglass batts. “I would guess that the foam being shredded and mixed with the cellulose would at least postpone its getting to the landfill," Klingel wrote, “and in the meantime it could be doing some good. No?”
Actually, no, said Katie, who identifies herself as a spray foam contractor. Katie backed up Holladay's analysis. “We wouldn't recommend shredding up open-cell waste and putting it in your attic (or anywhere, really), for all the reasons discussed: fire hazard, no air barrierBuilding assembly components that work as a system to restrict air flow through the building envelope. Air barriers may or may not act as a vapor barrier. The air barrier can be on the exterior, the interior of the assembly, or both., no insulation value,” Katie wrote. “Plus, dust particulate would be an issue. We once tried putting open-cell waste in our fiberglass blowing hopper to shred it up and blow it in an open space just to see what would happen and if it could be done. The hopper reduced the insulation to fine pellets and there was a ton of dust. Hardly worth the time or effort to ‘recycle’ the foam when the only thing you'll gain is a fire waiting to happen.”
Whose responsibility is it?
Halkias wrote the contractor stipulated in his contract that he would bag the waste and clean up the site, but would not be responsible for disposal. “This being my first spray foam experience, I did not realize the waste that would be generated,” he said.
Whether the contractor was upfront about it or not, leaving waste materials behind for the homeowner to deal with seems an odd exception in the building trades. Offcuts from framing lumber, drywall scraps, plumbing and wiring odds and ends and all the other debris from construction is usually taken away by the sub, or at least pitched into an on-site Dumpster by the general contractor.
“I think that any spray foam contractor who doesn't take responsibility for job waste is irresponsible,” wrote Holladay. “One way of shaming this contractor is to name the company and the city. Any company that claims to be environmentally responsible should have a waste disposal plan,” he added. “If a contractor's routine work generates waste, then disposing of that waste in a responsible manner should be part of the contractor's routine services — in my opinion.”
“Every construction or remodeling contract should end: ‘The site will be left broom clean,’ ” said Robert Riversong.
But maybe the practice is common in some areas. John Brooks said the practice of charging to haul away foam waste is common in North Texas, according to the contractors he's spoken with. “The amount of waste with an open-cell job can be LARGE,” he said. "Not only is there a FEE ... there is a high volume of foam filling up the landfill.”
What should be done with scrap foam?
“Open-cell spray foam is mostly comprised of air and is completely safe to take to a landfill,” said Clark, whose post includes a link to Spray Foam Energy Solutions, a California company. “It will crush down to almost nothing when driven over with tractors commonly used to compact the waste stored there. Contrary to common belief, there is very little decomposition going on in the landfill except for food waste as a few minutes with Google will attest.”
And that's the problem, said Riversong.
“Plastics last virtually forever in landfills and elsewhere in the environment, including the great Atlantic and Pacific garbage patches, where they do break down in size, becoming smaller and more dangerous to the biosphere," Riversong added. "Green materials compost back into their natural constituents and become food for new life.
“And you're completely wrong about pieces of cured foam acting as an air barrier,” he continued. "It is an air barrier only when foamed in place or placed as a tightly-fitted and sealed rigid board.”
The potential for environmental and human damage from petrochemicals and chemical additives is troubling to some posters.
GBA advisor Michael Chandler, for instance, wrote, “The fire retardants in spray foam and board foam are a bio-accumulative neuro-toxin, so disposing of waste foam in a landfill is not doing the planet any favors.”
Like John Brooks, who wrote that he is moving away from foam, Chandler is looking for alternatives to spray foam and rigid polystyrene board in the houses he builds. “I'm not there yet,” he said, “but moving in that direction.”
Chandler attributes his change in thinking to some conversations he and his wife had with Arlene Bloom at the Build Well conference last year. “She and Theo Colburn really got me thinking about the unintended consequences of some of the chemicals we use in our pursuit of improved energy efficiency,” Chandler said.
Riversong added, “Of course we would not find ourselves so often surprised by the unintended consequences of our choices if we used the Precautionary Principle, which requires that any new thing be proven safe (and necessary) before introduction into the marketplace and environment, rather than waiting until someone discovers it to be unsafe. On that basis, it would be reasonable to assume that all 80,000 petrochemicals we've created, that never before existed on earth, are unsafe until proven otherwise.”
Industry “still in its infancy”
Some spray foam installers may be pushing spray-foam as the greenest thing since LEEDLeadership in Energy and Environmental Design. LEED for Homes is the residential green building program from the United States Green Building Council (USGBC). While this program is primarily designed for and applicable to new home projects, major gut rehabs can qualify. , but you won't find Katie among them.
“As a spray foam contractor, we are not in the habit of buying into the 'Foam is Green' marketing ploy and do not sell it as such,” she wrote. “We install open- and closed-cell spray foam for its high insulation value and air barrier qualities (when applicable) to people who can afford the upgrade. Period. We are honest with people who are considering foam: it's expensive, it's combustible, it's plastic, and the initial off-gassing (although more dangerous to installers than building owners) during install may be a nuisance to sensitive people.”
Still, she added, spray foam has some tremendous advantages.
“The spray foam industry is still in its infancy, and there's a long way to go until it becomes a respected and viable industry, like cellulose and fiberglass have,” Katie added. “Yes, there's a lot of waste with open-cell, no matter how good an installer you are. (Waste is different than overspray, by the way.) Yes, the product can't be reused and takes up a lot of space in landfills. But what insulation is truly green? None that we can think of.”
Our expert's opinion
Here's what GBA technical director Peter Yost had to say:
Insulation value in attic: I agree with Martin and Katie; there is no net gain to be accomplished with this effort.
Responsibility: Dealing with the overspray and cut-off waste definitely is the responsibility of the installation contractor and, as Riversong stated, easily covered by the standard “broom clean” contract language. And a really good reason for this is that if the contractor has to deal with the waste, what better way to ensure that the contractor has incentive to minimize this waste?
Cutting versus “roller-shaving:” Big difference between these two in terms of dust creation when removing the overspray. The dust from roller-shaving the excess can be substantial and pervasive, making for a nuisance to most of us, and a health issue for sensitive individuals. When we used open-spray foam to insulate exterior walls in our own basement, the excess was roller-shaved. While the contractor left the basement broom clean, an acrid dust covered just about everything and proved to be a real problem for our daughter with asthma. After a full day of HEPA-vacuuming every exposed surface we were fine, but cutting at least most of the excess would have created a lot less dust.
Spray foam insulation contractor certification: In Canada, this is required. The U.S. needs mandatory spray foam insulation contractor certification to separate the wheat from the chaff.
Flame retardants: While open-cell spray foams have a good profile in terms of global warming potential they typically contain brominated flame retardants as Chandler pointed out. Selecting the most benign and highest performing insulation remains a real challenge.
Mon, 01/17/2011 - 12:56
"a concurrent thread"
by John Brooks
Some people have noticed that the "Not-So-Foamy" discussion is not only about Spray Foam.
It is about ALL foam products.
Edit to add soundtrack
http://www.youtube.com/watch?v=1PK2R0IwCiY
Mon, 01/17/2011 - 13:05
Attic Spray Foam Insulation
by Green Mountain Realty
We like spray foam in the walls but are not as convinced in the attic thats the best way to go.
Mon, 01/17/2011 - 13:07
risking criticism here for challenging Anonymous Posters
by John Brooks
I can not help but notice that "Katie" (an anonymous poster) has not returned to answer any further questions.
Mon, 01/17/2011 - 13:09
What insulation is truely green?
by ROY HARMON
Straw, used as a building material and insulation is probably as green as it gets.
Something not promoted as much as toxic foam. Far from green...
Mon, 01/17/2011 - 13:26
Industry still in it's infancy...
by ROY HARMON
Seems that the cart has been put in front of the horse on this one folks. all of the toxic waste and nowhere to put it... gosh, I wish I would thought of that one sooner.
Hard to imagine anyone involved in "green building" would still be on the fence with this one.
No brainer people. Toxic ain't green !
Mon, 01/17/2011 - 13:29
BioBased foam an alternative?
by Rob
I remember reading about soybean-based foam and seeing a brief publicity blitz about it last year. I'm not in any position to judge its overall green-ness, though. Has anyone had any experience with companies that offer that service?
Mon, 01/17/2011 - 14:42
Soy Foam
by ROY HARMON
All spray foam insulations are petroleum based. Including soy foam insulation. The maximum soy content in these foams is 15% and they generally cost 3 times more than regular foam insulation.
They are available in both open and closed cell with opencell naturally being less expensive. Still lots of questionable chemical stuff going on in both sides of these mixes.
Put a handful of soybeans into a gallon of oil to judge the greeness.
Mon, 01/17/2011 - 23:32
RobThere is not a great
by Robert Hronek
Rob
There is not a great reduction in oil used in production. An applicator told me about 15% soy based.
As far as the scrap waste. I think just laying the pieces on top would do little. It is not the air move through the material it is the air moving around the material. MY thought was what about laying the foam out and then covering with cellulose, fill the voids between the foam and have a covering over the foam. Since we are talking about bats covering with cellulose should help. Plus there is probably exposed rafters and thermal bridging. This is probably better than just putting the foam in a landfill.
Tue, 01/18/2011 - 02:35
soy foam and off-ratio issues, proposed change to NGBS and LEEDh
by Michael Chandler, GBA Advisor
We've noticed more problems with mix consistency with bio-based foams leading to persistent odor and inconsistent hardening. The quality of the training of the installation crew is a big factor here.
I've been continuing to dig deeper into the flame retardant issue and have a proposal in for the ANSI-700 NGBS re-write that is currently worded as follows:
Chapter 9 Indoor Environmental Quality 901.11 Insulation Add new as follows:
901.11 (C) Environmentally preferable flame retardant used exclusively in foam board and spray foam insulation products.
Less environmentally persistent, bio-accumulative and neuro-toxic flame retardant additives are specified and implemented exclusively such as non-halogenated, bio-degradable Triethyl phosphate (TEP) or persistent and halogenated but less toxic Tris (1-chloro-2-propyl) phosphate (TCPP).
Reason:
Many of the flame retardants currently in use have been linked to endocrine disruption and birth defects. Their absorption in to the system through dust or direct skin contact can be very rapid, long lasting, and can be associated with birth defects such as reduced birth weight and delayed secondary sexual development especially in male infants. At this point there is no incentive for flame retardant manufacturers to disclose which of the legally allowable chemicals they use in their products so consumers have difficulty identifying preferable products as the MSDS sheets list flame retardant composition as "trade secret."
Offering point credit for products that can verify that preferable chemicals were used could lead to a premium class of flame retardants in foam insulation panels and in spray foam both open and closed cell, as well as home furnishings foam, carpet and fabrics, and could help ensure the health of future generations as well as the children born in these cleaner homes.
Tue, 01/18/2011 - 12:55
Point credit?
by ROY HARMON
What point credit? Is there such a carrott to dangle? At whose expence?
Dangerous chemicals will remain dangerous chemicals~ I don't get the point.
Tue, 01/18/2011 - 18:45
Point credit
Roy the idea I'm proposing here is to use the National Green Building Standard and LEED-h as incentives to convince industries that are required by law to add flame retardants to their products (Board foam, Spray foam, Carpet, Carpet pad, Laptop computers, Televisions, foam upholstered furniture, curtains, etc. ad nauseum. to stop listing "trade secret" as the fire retardant of choice in their MSDS reports and start actually disclosing what they are using and eventually use market forces to encourage them to use less toxic and environmentally persistent and accumulative products.
There are many people here who are not aware of the hazards involved with building or furnishing a home. Those who are aware that , for instance the computer I am typing this on is loaded with flame retardant, or that the chemical content of the spray foams, board foams, carpet or flooring products I use in my homes are rarely disclosed in the MSDS report.
Some may simply decide to live without TVs, computers, cars, foam products or uphlstered furniture but there is power here to encourage more open disclosure and move the industry to find and use environmentally preferable solutions. They have no incentive if there is no disclosure or no market. LEED-h and ANSI-700 NGBS were designed to effect market change. Both are in re-write at this time. Now is our chance to raise the bar to those definitions of green and move us towards a less toxic solution.
It is legal to hide the presence of toxic elements in your products behind the "trade secret" mask in the MSDS. Making certain chemicals illegal has been disastrous, we are faced with endocrine disrupting and bio-accumulative halogenated flame retardants because previous flame retardants were found to be carcinogenic so the legislators demanded that industry find replacements that are not carcinogenic. Rather than say "don't use this" with out offering an alternative we are better served by finding a preferable solution and encouraging the industry to switch.
I'm done making babies, this is not about me. It doesn't matter if I take a nap on an upholstered sofa or wrestle with my kids on a nice new carpet. It matters to future generations, and the path to a less toxic marketplace is through codes and standards. LEED and NGBS may not be "green" by the measure of the majority of folks on this site but they have great sway in the market. they are the tools we can use to implement change.
Tue, 01/18/2011 - 19:05
Point Credit
by ROY HARMON
Thanks for the explanation Michael,
If trade secrets can be revealed on MSDS papers that would be a step in the right direction.
I would venture a guess that most consumers don't know what a MSDS sheet is though. Still, having the truth in writing would create a degree of accountability that does not exist now.
Good idea.
Wed, 01/19/2011 - 09:33
foam
by David Lanfear
I understand that that people want to use foam for performance reasons, but all he negatives greatly outweigh that performance. the unknown effects of the chemicals, the lack of bio-availability for future decomposition, waste disposal issues, fire hazard(I didn't know this) and the most overlooked, future deconstructibility. A foamed house has been essentially glued together rendering all framing and sheathing components unsalvagable in the future, which guarantees more wastes in a land fill.
Even SIPs have some potential for being reused at some point, though they have their drawbacks.
There seems a constant struggle against market forces which may move us towards one goal(a buildings energy efficiency) but away from others, like sustainable material loops.
Wed, 01/19/2011 - 10:39
Spray Foam
by Katie
Mr. John Brooks -- allow "Katie" to introduce herself. I am the marketing manager for Tridon Industries, an installer of spray foam and other types of insulation, as well as fireproofing, in residential and commercial applications. We are based in suburban Philadelphia, and service the Northeast and Mid-Atlantic regions. Pleased to meet all of you!
I haven't found a way to "follow" this thread, or set it up as an RSS feed, so therefore have had to rely on my memory to bring me back here for further comments. Also, it seems the first time I commented, I got so wrapped up in the swirl of the conversation I neglected to attribute myself. My apologies.
We've been installing spray foam for nearly a decade, and in that time have installed just about every product from every manufacturer you can think of. We were installing spray foam long before it became the popular thing to do, and long before the "green" movement became de rigueur, because we believed in it. And we still do, for all its benefits. Of course you need to maintain perspective -- Installing spray foam is no more hazardous than crab fishing or mining for coal (jobs we still deem essential), in that there is the potential for illness and toxicity and long-term side effects. It's all about having a work force that is trained and knowledgeable and protected as best as possible against danger.
In nearly a decade of spraying foam, however, we've had little complaint from any customer, other than the smell, from allergy/asthma sufferers. The vast majority of our customers are pleased with the outcome -- lower energy bills, less drafts, etc. We still believe that spray foam is more a nuisance to installers when it's being applied than the cured foam is to building occupants once the job is all said and done. That being said, we continue to push the manufacturers we deal with for disclosure on such things as chemical ingredients and soy content, and find that they're starting to come around. Mr. Harmon / Mr. Chandler: I thought you might find that tidbit especially encouraging.
We welcome any open dialog about spray foam--good and bad--as the industry continues to grow.
Katie McVay
Marketing Manager
Tridon Industries
Wed, 01/19/2011 - 10:51
Response to Katie McVay
Katie,
Once again, I'd like to thank you for your comments.
Wed, 01/19/2011 - 12:27
I will Second That
by John Brooks
Katie,
Thank you for your comments.
I thought you were a hit and run poster.
It turns out that you are not.
thank you for returning and responding to my questions.
Wed, 01/19/2011 - 15:18
Foam Alternatives
by Allan Bullis
Discussion on landfill and toxin issues of foam has been great. These are detriments to foam, in addition to the fact that in many cases installed foam is compromised due to environmental conditions during installation, shrinkage, and air-leakage. (yes there is leakage if not installed properly) All told these facts re-enforce my thoughts that cellulose in walls and attic is the best choice.
Wed, 01/19/2011 - 15:28
Spray Foam Versus Blown Cellulose
by Kurt In Seattle
My preference is Dense Packed Blown Cellulose because of all the complications, doubts, hassles and environmental impacts of spray foam. I'd be curious to hear others thoughts on the comparison between cellulose and spray foam.
Wed, 01/19/2011 - 15:42
Response to Kurt
Kurt,
If you use the "search" feature on the GBA Web site, you'll find plenty of articles and Q&A discussions on cellulose vs. spray foam.
Wed, 01/19/2011 - 15:46
open cell waste
by Steve Richards
Our industry has been looking for the magic answer as to what to do with open cell cutoffs, and in fact, there is a current article in Spray Foam magazine dealing with this issue. I hope as the problem is discussed further, someone does find a solution. My primary concern of course is that anything that lands on the floor does so at great cost to the contractor, as the typical 3500sf home sees hundreds of dollars worth of material (OC) go in the dumpster, in the form of offcuts.
As for leaving jobsites with all of the cutoffs, it's virtually impossible, and anyone who expects a spray foam contractor to do so on every job lacks intimate knowledge of the business of an SPF contractor. Spraying a different large job every day generates enough waste that the contractor would need a full time waste disposal crew with truck(s). Then the foam would end up being disposed of through the same channels as the homeowner or GC would, so we'd all rather pass the savings along. If we're asked to take it, by all means, we'll arrange a dumpster at the jobsite's expense, but just about every person I've met would rather not pay hundreds of dollars for this service. And I would hope to be spared the argument that only multimillion dollar businesses with full time garbage crews, multiple dumpsters, etc. should engage in spray foam. Small businesses, besides being the lifeblood of the country, bring a wealth of experience, knowledge, and personalized service/attn. to detail to the table that most larger competitors can't match.
Wed, 01/19/2011 - 15:54
Response to Steve Richards
Steve,
The fact that you feel that removing the waste generated by your work from the job site would be "virtually impossible" doesn't speak well of the industry.
When I worked as a contractor, I was responsible for all the waste generated on the job site, and I expected the same from other contractors working there. Like you, I hope that "someone finds a solution" to this problem. In the meantime, I think two first steps would be for contractors to endeavor to minimize the foam that expands beyond the studs, and to take responsibility for cleanup and disposal.
Wed, 01/19/2011 - 15:55
flammability
by Steve Richards
I forgot to mention... I understand that spray foams are recognized as a combustible material, and I by no means dispute that. However, I would suggest that anyone commenting on flammability of spray foams at least try burning a sample. Most commercially applied spray foams will not support a flame once an ignition source is removed, and it is a source of struggle for our industry that we are placed in the same category as much more dangerous products such as expanded polystyrene (EPS - the white stuff, which burns, melts into a liquid, etc). I'd like to see a realistic understanding among the building community as to the combustible nature of polyurethane/polyiso vs polystyrene foams.
Wed, 01/19/2011 - 16:16
open cell waste
by Mark Brannkarr
Why can't these scraps be placed in a cavtiy/bay and sprayed over?
Wed, 01/19/2011 - 16:39
Response to Mark Brannkarr
Mark,
You asked, "Why can't these scraps be placed in a cavtiy/bay and sprayed over?"
1. Most spray foam installations are in wall cavities or sloped ceilings, where gravity would prevent your proposal from being carried out.
2. While your proposal would work on an attic floor, most attic floors are insulated with less expensive insulation materials like cellulose.
Wed, 01/19/2011 - 18:26
foam scrap
by Steve McCarthy
I see no problem with blowing cellulose over foam scrap in a flat ceiling attic. I do it regularly.
In my business, I never use two part spray foam. I am a retrofitter and much of my air sealing effort uses one part foam and rigid foam board that is mostly isocyanurate. I generate scrap and I will not throw this stuff in the dump. In houses with 3-6" of existing insulation, I lay the scraps flat and blow at least 6" over them. In my case, the foam might replace 25 pounds of cellulose at the most. I do the same with scrap fiberglass with the kraft removed.
I have never seen how much waste is generated in a new construction wall foam project but if it could be covered with enough cellulose, I see no good reason to put it in the landfill. I don't think it will do any good to spread it over existing fiberglass batts and blown fiberglass should be banned.
Several years ago some local firefighters were called to a house fire. The homeowner worked in a shipping department of a local business and had saved used foam peanuts and packing foam and then put it in his attic. It was the only insulation in the attic and the only ceiling was the grid type that is used mostly in commercial buildings. The foam in the attic melted before it burned and the stuff dripping thru the ceiling made it very difficult for the firefighters.
Wed, 01/19/2011 - 19:45
Hmmm...
by Lucas Durand - 7A
Steve, do you not see anything backwards in this shoot first, ask questions later approach that the industry takes?
Thu, 01/20/2011 - 12:47
Incinerator vs. landfill for foam scraps?
by Anita Brosius-Scott
Here in Maine, our municipal waste - that which cannot be recycled (or that which people are too lazy to separate out), is hauled to an incinerator and burned, the gases scrubbed of toxins in the smokestack. Or so they assure me. The energy thus released is used to generate electricity - though that source ends up being only 0.9% of the electrical energy source for our domestic use.
The above discussion of the end-of-the-line for waste foam consistently references landfill disposal.
I don't know how common electricity-generating municipal waste incinerators are nationally, so this option may not be readily available in other communities. But I'm hoping that tossing my foam waste into that hopper is "better," all things considered, than putting them in a landfill.
I went through great knashing of teeth in considering how to insulate our basement; David Lanfear's comment reflects strongly one of my major concerns: how foaming renders an otherwise innocuous assembly of house parts unrecyclable, unusable and toxic upon deconstruction.
I am in the process of cleaning out and renovating a "basket case" of a house (not our home), formerly belonging to compulsive hoarders. As a hopelessly compulsive recycler, I wish to render each "trash" item to its highest and best use, even bits of wood. It is AMAZING how little actually ends up in our landfill when the contents are disposed of conscientiously. In my perspective, we are indeed borrowing the Earth from our grandchildren and have an obligation to take good care of it. There is no "away," as in "throw away." It takes more time, but when considering the value of my time, I consider it in the context "as opposed to the value of the environment which I affect." The environment usually comes out ahead in priority.
This discussion is a VERY IMPORTANT one that needs to take place, and the problems discussed regarding the use of foams need to be addressed in such a way as to minimize damage to the earth and our environment at all phases of the product's "life."
Fri, 01/21/2011 - 00:48
Spray foam
by Steven
idea, though dealing with scrap is an issue one result would be to grind it up and than blend back into componets for spray at next site or onsite. Now understand this is only an idea that comes form dealing with polyester scrap and thermoset scrap (think bondo) in that this scrap now acts as a filler.
again testing and research must be done, more from suppliers side.. May change density, but would be worth testing..
Fri, 01/21/2011 - 12:48
recycling poly offcuts
by Casey
These offcuts could be collected and stabilized in additional foam, or in large fabric wrapped bales. Then used as lightweight fill in large architectural projects. Such as buildings' planter areas, freeway interchanges, large concrete formworks.
Fri, 01/21/2011 - 14:47
Foam waste as soil amendment
by William Young
I am curious if open cell foam waste could be used as a soil amendment. I wouldn't break down so it offers body to soils like clay and it holds water so it would release it slowly instead of draining away. This might allow one to "feed two birds with one scone".
Also, I haven't heard anyone talk about Airkrete in the foam discussion. It also fills the cavity, offers a minimal air barrier, offers sound deadening and is fire retardant. It doesn't provide as high an R-value as petro-foam, but at least is not toxic and it's waste components make disposal less alarming. I have been in the room while it was being sprayed and it smelled like the ocean, but it didn't cause any discomfort. Anyone have any experience with this product?
Fri, 01/21/2011 - 17:57
What I did with scrap / cut off insulation
by Mark Bartosik
I have been storing scrap / off cuts of 1" and 2" thick polyiso and XPS boards (not scrap spray foam off cuts).
So this past weekend used these scraps to rough fill the interior of a 200 sq ft 2x4 wall. I stuck the scraps onto the nails that were sticking through the inside of the sheathing. I left about 1" to 2" gap around the edge between the insulation and the studs (with hindsight only about 3/4" to 1" was needed). I did not expect this by itself to help with air sealing or even add 1 to the R value of the wall.
Then I used 200 board feet of 2 part foam to foam in place the rigid scraps of XPS and polyiso.
I used the scraps to fill the bulk area, and new spray foam to air seal around and bind the scraps in place. Thus I filled about 3" deep on average over 200 sq ft, that would have normally used 600 board feet of new foam, but only needed 200 board feet of new foam. Thus saving over $300 in spray foam, resources, and saving from land fill a load of polyiso and XPS, at the cost of about a man day of labor. (I value my labor above that so maybe I lost on this deal, but I'm happy with the outcome).
This was the first time that I had used 2 part spray foam myself (I had watched contractors use it before).
The down side is that I needed to inspect after for a few holes that I missed, and it was labor intensive to pack the wall with the scraps. I suspect I'll use about 2 cans of 1 part foam to touch up a few places I didn't do so well (probably only because I was inexperienced with using 2 part foam).
This is actually the second wall I have packed with scrap insulation. The first I tried using expanded polystyrene peanuts that I accumulated free over years from various packing materials (I only had enough for one 2x4 bay then).
I think that if insulation cut offs are embedded in the middle of other insulation then it can work well to reduce the volume of new insulation, but it needs to be surrounded with new insulation.
Mon, 01/24/2011 - 22:13
foam in the attic
by Walter Wardrop
I built my ICF home back in 2005. The attic has a 7 inch layer of expanding foam sprayed into a standard 4:1 truss roof. I then threw about a foot of scrap foam onto this layer of virgin material. To prevent animal and fire risk, we blew 12 inches of fibreglass to make a sandwich. So all together, there are 3 layers. Base layer is the expanding foam, middle is scrap foam from my site and others, and top sealing layer is the 12 inches of fiberglass. Note that one of the best things we did was build a runway through the attic for the workers (and myself) to work from. I am pretty sure I got a lot more than 12 inches of fibreglass, as the installer just blew the stuff in until it reached my runway. My table napkin estimate is R65 in the eaves to R80 in the centre. Checked it last year and there was no sign of settling.