0 Helpful?

Should I use a poly-type Membrain sheet or vapor retarder paint for ceiling?

I'm at a crossroads with how to deal with the ceiling vapor retarder in my new construction home in climate zone 5.

I'm prepping for drywall, and am wondering if I should apply Certainteed Membrain vapor barrier to the underside of the studs on the ceiling, and then just have the ceiling drywall screw attached...

-or-

Should I have the ceiling drywall glued and screwed and use vapor retarder paint instead.

I plan on blowing R60 cellulose in the attic when done, and am concerned about it's weight on the drywall.

Most drywall installers I've talked to advise against using glue. For one it adds more cost, and it will also be difficult to repair any damages in the future.

I've seen Bill Hulstrunk's comment about successful experience of adding R100 to the ceiling without any sagging issues, but I wonder if he was just screwing, or using glue as well?

Asked by Adam Peterson
Posted Nov 14, 2017 4:42 PM ET

Tags:

2 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

What is the spacing on your rafters, and the thickness of your drywall?

A similar questions was discussed in this thread: http://www.greenbuildingadvisor.com/community/forum/green-building-techn...

Answered by Steve Knapp CZ 3A Georgia
Posted Nov 14, 2017 7:35 PM ET

2.

In zone 5 there is no need for a ceiling vapor retarder with a vented attic design. Air tightness still matters though.

Using ring shank nails for the gypsum board is usually enough for managing the weight of deeper cellulose than R60, no need for glue. If it's a 24" o.c. truss design rather than 16" o.c. joists, install 1x strapping 16" o.c. perpendicular to the truss chords with screws or ring shank nails (shimmed for ceiling flatness), and ring-shank the gypsum to the strapping.

Answered by Dana Dorsett
Posted Nov 15, 2017 4:47 PM ET

Other Questions in Green building techniques

Ranch vs 2-Story Home

In Green building techniques | Asked by Peter L | Nov 16, 17

1-1/2" wide rigid foam strips on interior of wall studs?

In Energy efficiency and durability | Asked by Brian Ducharme | Nov 17, 17

Primary Damper for Tulikivi wood stove?

In General questions | Asked by jim sweazey | Nov 17, 17

Site built ventilation baffle moisture issue

In General questions | Asked by Michael Prisco | Nov 17, 17

Flat roof attic insulation

In Energy efficiency and durability | Asked by michaeldrehl | Nov 17, 17
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!