What are all the factors in determining if we should place rigid insulation on the INSIDE of a poured concrete foundation wall OR on the OUTSIDE?

user-1112730186 | Posted in Green Building Techniques on

Cold climate (Chicago region).

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Expert Member
    Dana Dorsett | | #1

    Cost

    insulation type

    exterior finish type on the foundation

    thermal bridging at the foundation sill & band joist

    siding type

    intended total R-value

    Performance wise it's often useful to keep the thermal mass of the concrete fully inside the thermal boundary of the house, and exterior foam on the foundation aligned with a foam-clad upper story wall can make a seamless thermal break at the band joist & foundation walls.

    But with brick-veneer houses you can't get the continuous foam, suffering a huge thermal bridge at the foundation top, and performance can be better with an interior foam aproach.

    Also, if you're insulating the slab it's easier to get a continuous thermal break at the slab/wall interface with an interior side foam approach, with the slab-foam meeting the wall-foam, "floating" the slab.

    Polyiso can be used on the interior side only for below grad apps due to it's slightly hygroscopic nature. Wedged between dirt & concrete it'll almost always saturate over time, losing a large fraction of it's thermal performance. EPS does much better, and is preferable to XPS on a number of basis'.

    Insulated concrete forms (ICF) give you something of the best of both worlds- for a price. From a "time is money" perspective it speeds up the whole process of an insulated foundation, but from a raw assembled cost it's usually a bit more expensive than an insulate-from-the-inside-only approach. A bare-bones ICF starts at R16 (R8 inside, R8 outside), and plenty for foundation insulation in a US zone 5 climate, but R20s are pretty common and may not be a big up-charge (if any).

    Only if you're looking for VERY high performance (Net Zero Energy, PassiveHouse certification, etc.) would going much over R20 make much sense in that climate, and even R20 might be a stretch.

  2. user-1112730186 | | #2

    Thanks. How much do you consider interior condensation on a concrete wall if you go with an exterior foam approach?

  3. Expert Member
    Dana Dorsett | | #3

    With an exterior foam approach the concrete is inside the thermal envelope where it's warm. If the concrete is cool enough to condense moisture out of the air, so is everything else in the room. At normal healthy interior humidity of say 35% RH @ 68F the dew point of that air is ~39F, a temperature the concrete will never reach when it's inside the insulation.

    With healthy 50% RH @ 75Fconditioned air the dew point of that air is ~55F, again a temp the concrete won't be experiencing in a 75F room when it's inside the insulation.

  4. user-1112730186 | | #4

    Interesting to note the following building science recommendation with much suggestion for the interior application:

    http://www.buildingscience.com/documents/information-sheets/basement-insulation/files/bscinfo_511_basement_insulation.pdf

  5. GBA Editor
    Martin Holladay | | #5

    Heather,
    In the following article, I provide a list of the pluses and minuses of both insulation approaches (on the interior of a basement wall or on the exterior of a basement wall): How to Insulate a Basement Wall.