Video: Superinsulating a Home With Rigid Foam

A THICK SKIN THAT KEEPS A HOME WARM AND DRY

What to think about when considering exterior insulation

BY GARY BERGERON

SheathingMaterial, usually plywood or oriented strand board (OSB), but sometimes wooden boards, installed on the exterior of wall studs, rafters, or roof trusses; siding or roofing installed on the sheathing—sometimes over strapping to create a rainscreen. with foam-board insulation is a great way to get more R-valueMeasure of resistance to heat flow; the higher the R-value, the lower the heat loss. The inverse of U-factor. with a conventionally framed house. It can work just as well in remodeling projects as in new construction. Applying rigid foam takes some getting used to, but the basic tasks are not that much different from installing typical plywood or OSB sheathing—and the lightweight foam is easier on your back. The biggest differences are in how you detail windows and doors and how you fasten and seal the foam boards to the wall. Rigid foam can be the insulation, air barrierBuilding assembly components that work as a system to restrict air flow through the building envelope. Air barriers may or may not act as a vapor barrier. The air barrier can be on the exterior, the interior of the assembly, or both., and drainage planePath that water would take over the building envelope. Concealed drainage-plane materials, such as building paper or housewrap, are designed to shed water that penetrates the building’s cladding. Drainage planes are installed to overlap in shingle fashion (weatherlap) so that water flows downward and away from the building envelope. all rolled into one. Pay attention to the details and seal every possible air leak, and you will end up with a more durable and energy-efficient home.

Some things to think about when planning to use exterior foam insulation:

Foam panels don't provide shear strength
Rigid foam can replace plywood wall sheathing, but it can't replace the strength associated with it. You still need to include some sort of bracing for this. Your engineer can specify where the shear panels or diagonal bracing needs to be. If plywood panels are used for shear strength, cover them with thinner layers of foam; this will keep the overall wall thickness consistent.

Extend the rough openings with a plywood box
Window and door rough openings get plywood boxes that extend from the inside edge of the wall to the outer edge of the foam sheathing. This allows you to mount the windows and doors flush to the outside of the wall. Be sure to compensate for the thickness of the plywood when you frame rough openings. Flash the windows to the foam with flexible flashing tape or some other window flashing system.

The right tool for the right cut
Straight, long cuts can be made easily with a tablesaw or circular saw. Long-bladed utility knives and small handsaws are great for tighter cuts and for adjusting the fit after the foam board is in place.

Effective air-sealing begins with a tight fit
Staggering the seams (two sheets of 2-inch foam, in this case) and taping the joints are important, but where foam butts windows, doors, and corners, the fit should be snug—tape shouldn't span cracks—so it's important to measure and cut carefully. Before installing the foam, run a bead of caulk where it will contact the top and bottom plates and the edges of walls. Be sure to tape all seams on each layer of foam, and flash to all windows and doors.

Tape sticks better on a clean surface
When cutting with a power saw, you will get a lot of dust on the boards. A paintbrush or a small dust brush works well to wipe dust off seams so that the tape adheres perfectly.

Continuous insulation is simpler and better
In the case where there's a first-floor bump-out with a roof that intersects a second-floor wall, run the foam sheathing down to the first-floor ceiling plane. Then fasten rafters and ledgers through the foam to the adjacent wall framing, and build the roof. This way the wall maintains the full R-value right up to where it contacts the insulation in the roof or ceiling plane.

Fasteners, flashing, and furring will be covered in future videos in this series.

—Gary Bergeron is a partner at Synergy Companies Construction. The home in this video was designed by Building Science Corporation in partnership with the U.S. Department of Energy's Building America Program.

27.
Thu, 09/22/2011 - 04:32

Edited Thu, 09/22/2011 - 04:32.

Response to Lyle Axelarris
by Martin Holladay, GBA Advisor

Lyle,
Q. "Why do I see so much foil-faced rigid foam on the GBA website?"

A. Because most of that foam is polyisocyanurate, and because polyisocyanurate is the most environmentally benign of the three major types of rigid foam (EPS, XPS, and polyiso). Polyiso does not have any blowing agents with a high global warming potential or any brominated flame retardants.

Q. "The foil will only be effective at reflecting heat (in the form of radiation) when the foil is exposed to an air space."

A. That's true. If a builder is installing foil-faced polyiso on a wall with vertical furring strips used to create a rainscreen gap, there will be some thermal benefit from the outermost later of foil.

Q. "Having foil-faced rigid foam sandwiched in a wall assembly is a complete waste of foil."

A. True, but the foil has another benefit (in addition to sometimes acting as a radiant barrier): the foil is an effective air barrier that limits migration (evaporation) of the blowing-agent gases. The longer that these bubbles of blowing agent stay within the foam, the longer the R-value of the foam will stay high.

Q. "Furthermore, the presence of the foil (which is a highly effective vapor retarder) in the middle of a wall assembly creates the 'double vapor barrier' no-no that we, in the Interior of Alaska, are trained vehemently to avoid."

A. When you have a stack of foil-faced foam, the entire stack of foam is a vapor barrier. No vapor is going through the stack. It makes no difference whether there is one layer of foil or 6 layers of foil -- the permeance is the same (very, very low). The permeance of foil-faced polyiso is 0.05 perm. So, there is no harm from stacking foam. It acts as a unit, and it is a vapor barrier.

Q. "This traps moisture in the wall cavity."

A. No it doesn't. If properly designed, a wall with rigid foam sheathing dries in both directions. Everything on the exterior side of the foam (the furring strips and the siding) dries to the exterior, while everything on the interior side of the foam (the OSB, the studs, and the drywall) dries to the interior.

Q. "Using foil-faced foam for header insulation (for example), when there is also a poly VR employed creates a moisture trap inside your wall cavity then I never understood the justification for."

A. If you choose to use rigid foam wall sheathing, then using polyethylene on the interior is a no-no. Even in Alaska.

Q. "Can you please clarify why the rigid boards in this video (and elsewhere on the site) are foil-faced?"

A. That's the way the manufacturers sell them.

Q. "In particular relevance to this article is their REMOTE wall system."

A. I have written many articles on the REMOTE and PERSIST wall systems. Here is one of them: Getting Insulation Out of Your Walls and Ceilings.


26.
Wed, 09/21/2011 - 19:23

foil facing and REMOTE walls
by Lyle Axelarris

Two comments/questions:
1. Why do I see so much foil-faced rigid foam on the GBA website? My understanding (from Thermodynamics) is that radiation "is considered to be a surface phenomenon for solids that are opaque to thermal radiation...", so the foil will only be effective at reflecting heat (in the form of radiation) when the foil is exposed to an air space. As such, having foil-faced rigid foam sandwiched in a wall assembly is a complete waste of foil (this was all confirmed by several PhDs in Mech. Engineering that I consulted with). Furthermore, the presence of the foil (which is a highly effective vapor retarder) in the middle of a wall assembly creates the "double vapor barrier" no-no that we, in the Interior of Alaska, are trained vehemently to avoid. This traps moisture in the wall cavity and serves no purpose (in our climate, at least). In this particular case, it may not be problematic, because in between each layer of exterior rigid foam is a drainage plane and the moisture won't move back into the framing, but using foil-faced foam for header insulation (for example), when there is also a poly VR employed creates a moisture trap inside your wall cavity then I never understood the justification for. Can you please clarify why the rigid boards in this video (and elsewhere on the site) are foil-faced?

2. One of the very few things that I think Alaska is ahead of the lower 48 about is air sealing and ventilation. The thermal and vapor gradients are so enormous here that it has just simply demanded that we pay attention to these details a long time ago. I encourage everyone to check out the Alaska Building Science Network and also the Cold Climate Housing Research Center, which is becoming world-renown for their advancement of cold-climate building science and alternative technologies for extreme climates in remote locations like all of our native villages. In particular relevance to this article is their "REMOTE" wall system. I do not work their, but shamelessly plug their information for the sake of advancement of energy efficiency:
http://www.cchrc.org/remote-walls


25.
Sun, 05/29/2011 - 15:27

Response to Eric
by Martin Holladay, GBA Advisor

Eric,
If you post your question on the GBA Q&A page, more readers will see you question and may offer answers:
https://www.greenbuildingadvisor.com/qa


24.
Sun, 05/29/2011 - 09:37

fasteners
by Eric Stonebraker

Hi GBA-
Very interested in your upcoming video on fasteners! When is it coming out? I have heard some concern by builders over fasteners for multiple layers of rigid foam. They prefer the simplicity of 1 layer of foam. Are there good options out there? I need something to convince some builders I am in discussion with. Any thoughts could help.


23.
Thu, 05/05/2011 - 09:52

Foam applications
by Jay Walsh

The issue of an interior vapor barrier may not me your choice to make. Be sure to check with your local building official in your area. If your stud cavity is filled with either friction fit fiberglass or cellulose and your local building code requires a "warm side in winter vapor barrier ..." your inspector may require it. He also might not consider the latex paint sufficient to meet this requirement. Of course you could try providing the official with some of the building science regarding your design, but in the end it will be up to him (or her).
Regarding internal foam applications, don't forget in addition to the deeper window jambs you also have electrical boxes to deal with, a real pain for your electrician. Also be sure everyone is on board with this design so you don't find out that your kitchen cabinets are too big by about 2" or issues with mounting due to the internal foam. Also, my experience with sheetrockers is that they will hate this job as you have created a great deal more work for them, in many ways.


22.
Sun, 01/30/2011 - 06:58

Edited Sun, 01/30/2011 - 06:59.

Response to Robert Dickinson
by Martin Holladay, GBA Advisor

Robert,
Q. "From a building science perspective, would it be good to have a class 3 vapor retarder on the inside, such as vapor retarder paint, to prevent much migration of moisture into the walls in the first place. Is that an improvement or a harm in that it would slow down drying to the inside?"

A. Either way will work -- with vapor-retarder paint or with ordinary latex paint. Either type of paint will allow some drying to the interior.

Q. "I'm wondering if there would be benefits to using one of the air-sealing membranes like that from SIGA."

A. In general, extra air sealing efforts are always good, although it's perfectly possible to achieve a high degree of air tightness at the sheathing level. To read about the pluses and minuses of the SIGA approach, see One Air Barrier or Two?.


21.
Sun, 01/30/2011 - 06:53

Response to CSolar
by Martin Holladay, GBA Advisor

CSolar,
Q. "I just want to make sure I understand this: with a sealed layer of foam on the exterior, there would be NO vapor barrier (poly sheeting) on the inside under the drywall, allowing the inside of the wall to dry to the inside. Is that right?"

A. Yes.

Q. "Secondly, I understand that condensation within the wall (in a cold climate) is not a problem because the exterior foam is thick enough that all the wall framing is above the dew point. If that's the case, then I suppose there's a minimum thickness required for the exterior foam, depending on the local climate? Are there published guidelines for that?"

A. Yes and yes. The guidelines are laid out here: Calculating the Minimum Thickness of Rigid Foam Sheathing.


20.
Sun, 01/30/2011 - 04:03

Air sealing a superinsulated house with rigid foam exterior
by Robert Dickinson

Martin,

Another great article.

I'll be adding two layers of 2" foil-faced polyiso shortly to a 1900 house. Staggered, taped seams, and housewrap as well, with the exterior details handled carefully. Interior stud cavities will be filled with cellulose.

Now, I completely understand why it would be dangerous to use a true vapor barrier like 6 mil poly on the inside. And I completely understand that my wall assemblies need an ability to dry in at least one direction, and in the case of exterior rigid foam, the only direction possible is to dry to the inside.

Now, what I am less certain about, from a building science perspective, is whether or not it would be good to have a class 3 vapor retarder on the inside, such as vapor retarder paint, to prevent much migration of moisture into the walls in the first place. Is that an improvement or a harm in that it would slow down drying to the inside? For my climate zone, marine 4, Eugene OR, with 4500 HDD, 4" of foam is plenty to avoid condensation on the interior side of the foam.

Another reason I ask is because this related to air sealing. I'm wondering if there would be benefits to using one of the air-sealing membranes like that from SIGA -- they have a vapor control membrane called Majpel 5 which is about 0.68 US perms which is typically installed on the interior.

I'm treating my exterior rigid foam insulation as my primary air-barrier, with taped OSB sheathing, taped foam, etc. And that ought to lead to a reasonably tight house -- especially considering the roof and underfloor measures I won't mention for brevity. But I am wondering if an air-sealing membrane, like that from SIGA, would be a good addition to the exterior air sealing in order to achieve even tighter ACH50 / CFM50 results.

Thanks for your insights.


19.
Wed, 01/19/2011 - 16:29

Understanding the vapor barrier situation
by csolar

I just want to make sure I understand this: with a sealed layer of foam on the exterior, there would be NO vapor barrier (poly sheeting) on the inside under the drywall, allowing the inside of the wall to dry to the inside. Is that right? (If that's the case, then it seems to me that the extra effort in sealing up the foam exterior is easily made up for by not having to install the interior barrier, sealing it around every junction box and window opening.)

Secondly, I understand that condensation within the wall (in a cold climate) is not a problem because the exterior foam is thick enough that all the wall framing is above the dew point. If that's the case, then I suppose there's a minimum thickness required for the exterior foam, depending on the local climate? Are there published guidelines for that?


18.
Sat, 01/01/2011 - 10:18

Response to Wayne
by Martin Holladay, GBA Advisor

Wayne,
You can install foam between your drywall and the studs if you want, although some installers don't like the fact that the foam makes the installation somewhat squishy. I have done it successfully with XPS and polyiso.

In general, exterior foam is preferred to interior foam, because exterior foam addresses thermal bridging at rim joists and partition intersections.


17.
Sat, 01/01/2011 - 09:41

using rigid styrofoam on the interior
by Wayne

I would like to know if it's ok to use rigid styrofoam insulation on the interior of a house. I was thinking of using it between the drywall and the studs, providing a thermal break and added insulation value. It seems to me that putting the styrofoam on the inside would be more benificial. Do building codes say not to do this?
Thanks


16.
Mon, 10/11/2010 - 04:10

Foam and brick ties
by Martin Holladay, GBA Advisor

Don,
You'll probably get more answers if you post your question on our Q&A page:
http://www.greenbuildingadvisor.com/qa


15.
Sun, 10/10/2010 - 22:07

Foam and brick veneer
by Don

I don't hear many discussions about thicknesses of foam board and brick veneer. Is there a sweet spot where a significant thickness of foam board can be used without incurring high costs of specialty brick ties?

I was designing a 3500 sq ft house (floor space) and coming up with $2500 in brick ties because of the distance of the brick from the OSB. I was assuming 1.5" foam and a 1" air space behind the brick.

I'm really more interested in general comments about brick over foam than addressing my situation specifically.

Thanks,


14.
Tue, 09/28/2010 - 05:50

Third response to Ennio D'Angela
by Martin Holladay, GBA Advisor

Ennio D'Angela,
Q. "Are there any detailed installation specs using exterior insulation, that I can provide to my builder/architect?"

A. Yes, We have a library of such installation details here at the GBA Web site. They are available to GBA members on this Web page:
http://www.greenbuildingadvisor.com/strategies-details


13.
Tue, 09/28/2010 - 05:48

Second response to Ennio D'Angela
by Martin Holladay, GBA Advisor

Ennio D'Angela,
Unless you are an experienced contractor, architect, or project manager, there is no easy way to develop the ability to provide cost estimates. If you want to estimate construction costs, you have two choices:
- Buy a cost estimating book (for example, one from R.S. Means) and use their cost data. This only makes sense if you have a good grounding in residential construction and a little common sense (so you can adjust the R.S. Means numbers for your geographical area).
- Contact some contractors and ask for bids.


12.
Mon, 09/27/2010 - 21:18

Changing Designer??
by Ennio D'Angela

Martin:
My designer may already be fully knowledgeable with exterior insulation and the cost benefits. I have not asked him. The reason I subscribed to Fine HomeBuilding is so that I can be as knowledgeable as possible when discussing this with the designer or the various other trades I will need to interact with in the process of constructing my new home. My reason for asking was to obtain the information. If you would assist me with obtaining this information, it would be most appreciated.
Thank you!


11.
Mon, 09/27/2010 - 10:22

Response to Ennio D'Angela
by Martin Holladay, GBA Advisor

Ennio D'Angela,
1. Any good architect or designer should be able to provide cost estimates for various design options. Such estimates are a routine part of architectural practice.

2. If your designer or architect is unfamiliar with the required details for exterior rigid foam, it's time to choose a new designer.


10.
Mon, 09/27/2010 - 09:57

Exterior Wall Insulation with a Brick/Stone Veneer.
by Ennio D'Angela

Hi Martin:
I plan to build a new large home next spring. It will have 2"x6" exterior framing with two floors. I am considering to have 4" exterior solid foam insulation and then 2.5" brick/stone over it with a 1.5" air space. There would be no internal 6mil poly as a vapour barrier. My concern is the extra complication of this external insulation method and extra 4" wider concrete foundation wall( more $$). Is there any cost/benefit study that compares external insulation with internal insulation when considering extra costs due to materials and labour? Are there any detailed installation specs using exterior insulation, that I can provide to my builder/architect? I live in Ontario Canada. Any help you can provide would be most appreciated.
Thank you,


9.
Mon, 09/27/2010 - 08:58

Response to Jason
by Martin Holladay, GBA Advisor

Jason,
You need to study some building science basics. Your thinking is at least 30 years out of date.

"Closed cell styrofoam is impermeable to water. So if you put it on the exterior of your house it acts as a vapor barrier, on the cold side of your wall. A big no-no."

Says who? As long as the siding can dry out the the exterior on the exterior side of the foam, and the wall assembly can dry to the interior on the interior side of the foam, what's the problem?

"The manufacturers say to leave a half inch air space away from your wall with venting top and bottom to prevent condensation."

What manufacturers? It's true that a ventilated rainscreen gap between the siding and the sheathing (or the foam) makes sense. The gap helps your siding to dry. But you never want to put a ventilated air gap between the wall assembly and your exterior foam.

"The practice of exterior-clad styrofoam should be banned where ever there is air temperature below freezing."

I'm sure glad that you don't have the authority to establish building codes, or else your ignorance would undermine energy-efficient building practices that help us all save energy.


8.
Mon, 09/27/2010 - 08:44

exterior foam
by jason

closed cell styro is impermeable to water. So if you put it on the exterior of your house it acts as a vapour barior, on the cold side of your wall. A big no no. the manufacturers say to leave a half inch air space away from your wall with venting top and bottom to prevent condensation, So if you do that the styro is not insulating anything at all.
The practice of exterior clad styro should be baned where ever there is air temp. bellow freezing, before we have nothing but rotten houses left.


7.
Fri, 09/24/2010 - 06:00

Response to Anonymous
by Martin Holladay, GBA Advisor

Anonymous,
Your biggest problem isn't the rigid foam; it's the air leakage. No insulation system can work well until you've addressed air leakage. So, if the ceiling area above the porch has air leaks, you need to track them down and address them first.

Once that's done, you can install rigid foam on your porch ceiling. However, you have to be sure that your rigid foam is thick enough. The colder the climate, the thicker the foam has to be to prevent condensation or moisture accumulation. Here's more information:
Easy Ways to Avoid Condensation in Your Walls


6.
Thu, 09/23/2010 - 22:17

outdoor porch ceiling
by Anonymous

is it wise to use 1.5" pink foam board insulation sheets against drywall on an old lath exterior porch ceiling with loose fill insulation and a heated floor above it? Do I need to worry about condensation on the foam board or drywall in a cold climate? What if the eaves of the porch roof allow air leakage in from the sides? The foam board forms a vapour barrier, and that's supposed to be on the warm side of any insulated wall, but there's the loose fill insulation between the floor joists above the porch. Would ordninary drywall be sufficient, or would I need to get cement board as my fire stop against the lath?


5.
Tue, 09/07/2010 - 10:21

Re: strapping and fasteners
by Rob Wotzak

NHSchreiner,
Synergy Construction typically uses pan head FastenMaster Headlok screws to fasten the strapping. These fasteners are sturdier than typical deck screws, but for thin layers of foam you could just use long deck screws. I've only seen folks use pressure treated strapping where it would contact masonry or other constant sources of moisture. Otherwise, standard furring strips or rips of plywood are fine, considering that the purpose for building this way is to allow for quick drying. If you've got any other questions you could stop by our Q&A forum (look for the Q&A tab at the top of every page).


4.
Mon, 09/06/2010 - 12:20

Retrofitting 1979 split with 1" rigid T&G insulation
by NHSchreiner

I am a furniture maker not a builder and am in need of some help. My 1979 split is a 2x4 framed house with no plywood sheathing just a layer of 1" rigid T&G blue foam on the exterior. I would like to remove the old Masonite siding and install an additional 1" foam, ventilation between the strapping and finish with Hardie plank siding. The reason for the ventilation barrier is I live in New Hampshire and the weather can be very damp at times. The north side of my house as all north sides gets no sun and is usually 5-10 degrees cooler, promoting mold and algae growth. What type of fasteners do you use to attach the strapping and does the strapping need to be pressure treated? Any help and or suggestions would be appreciated.


3.
Mon, 08/16/2010 - 15:40

Using foam as a WRB
by Martin Holladay, GBA Advisor

Mike,
Either XPS or foil-faced polyiso can be used as a WRB, as long as the seams and penetrations are detailed properly. If you choose this route, you don't need housewrap. Many builders, however, use both housewrap and rigid foam.

For more information, see
Using Rigid Foam As a WRB.


2.
Mon, 08/16/2010 - 15:27

Tyvek
by mike

Mr Joyce makes no mention of housewrap. Only to say the foam is our air barrier. Does this mean there is no need for housewrap. Is this because the foam is polyisocyanurate? what about other types of ridgid foam?


1.
Thu, 07/22/2010 - 22:48

Exterior Foam Retrofit
by Mark Miller

We are putting together an estimate for one of our clients to install Hardieboard siding. My client is very interested in energy efficiency, so I mentioned adding exterior foam insulation to help insulate their home. I'm wondering if anyone has any tips on a retrofit situation like this. Existing walls are 2x4, home was just re-insulated with blown in fiberglass recently (from the exterior). There are a plethora of windows, all will need boxed out in one way or another. I appreciate any ideas. Thanks.