guest-blogsheader image
0 Helpful?
Wolfe Island Passive: Adding the Insulation
With the shell up, work turns to installing the roof overhangs and the exterior insulation
Posted on Dec 29 2016 by David Murakami Wood
Editor's note: David and Kayo Murakami Wood are building what they hope will be Ontario's first certified Passive HouseA residential building construction standard requiring very low levels of air leakage, very high levels of insulation, and windows with a very low U-factor. Developed in the early 1990s by Bo Adamson and Wolfgang Feist, the standard is now promoted by the Passivhaus Institut in Darmstadt, Germany. To meet the standard, a home must have an infiltration rate no greater than 0.60 AC/H @ 50 pascals, a maximum annual heating energy use of 15 kWh per square meter (4,755 Btu per square foot), a maximum annual cooling energy use of 15 kWh per square meter (1.39 kWh per square foot), and maximum source energy use for all purposes of 120 kWh per square meter (11.1 kWh per square foot). The standard recommends, but does not require, a maximum design heating load of 10 W per square meter and windows with a maximum U-factor of 0.14. The Passivhaus standard was developed for buildings in central and northern Europe; efforts are underway to clarify the best techniques to achieve the standard for buildings in hot climates. on Wolfe Island, the largest of the Thousand Islands on the St. Lawrence River. They are documenting their work at their blog, Wolfe Island Passive House. For a list of earlier posts in this series, see the sidebar below.
The roof of our new house, like the exterior walls, is made with cross-laminated timber (CLT) panels, so it doesn't need any conventional framing. But we did need rafters at the perimeter of the roof to support the roof overhang, and the rafters had to be sanded and stained before they could be installed. In order to do that, we had to keep the temperature in the house above 10ºC (50°F), when it’s been down to -15ºC (5°F) outside, so the air heater inside has been vital. It’s somewhat ironic to think that keeping this temperature will be easy once we have the insulation on.
The roof overhang will shade the upper-story windows on the south side from direct summer sun — vital in preventing the house from overheating — while maximizing solar gain in the cooler months. Inside blinds don’t actually prevent summer overheating; while they act as a barrier to light, they still allow heat into the house. Outside blinds mean extra complications.
The veranda roof will do the same for the lower-story windows. The overhang also will make the roof area larger, enabling us to maximize our solar power generation (when we eventually fit the panels). Roof overhangs do many other useful jobs, however unfashionable they currently appear to be with architects who want their roof edges to be flush to the walls, largely for the sake of a "clean" look.
Given that we don’t need them to support anything more than the overhang, our rafters are short and are screwed into the CLT roof panels. The insulation will be cut to fit around them, and they will then be covered with an additional top layer of wood fiber insulation, then wide strapping, and finally the steel roofing. The strapping has to be sturdy enough to hold down the insulation as well as support the steel roofing and, eventually, the solar panels.
Adding insulation on the roof
The work was performed in February, during a warm spell — well above freezing — which means the crew has been able to get on with installing the rafters. While they were drying we also managed to wrap the whole house — finally — and just in time for what looks like very heavy snow and rain later this week.
In addition, with the house getting warmer, due to both the warm weather and the heating, the remaining water that had frozen inside the CLT structure after very heavy rains in January is coming out (for more on that problem, see the post from January 10, 2016). This is getting us closer to drying everything properly. Once that is done, we can put floors in.
We were expecting a return to more normal, and colder, temperatures as well as snow. But before all this hits us, the crew has had time to prepare for insulating the roof. This will need two things: cutting the wood fiber panels into the exact shapes required to fit in between the rafters; and devising a system for getting the heavy insulation panels where they are needed.
Both problems have been worked out. In particular, the crew managed to rig a combination trolley-pulley system using a ladder, that seems to work very well in getting the panels up to the roof (see Image #3, below). Now we just need some reasonable weather to get it done.
Exterior insulation is mostly wood fiber
For those who have been paying attention, you will recall that we are mainly using German-made Schneiderholz rigid wood fiber insulation boards. These are basically mashed up and reconstituted spruce and pine from sustainable sources.
They have an R-valueMeasure of resistance to heat flow; the higher the R-value, the lower the heat loss. The inverse of U-factor. of nearly 4 per inch, and we are using two layers on both walls and roof: a thick inner layer of 240 mm (9 1/2 inches) covered by a thinner outer layer of 40 mm (1 1/2 inches). The outer layer also has a coating that's relatively waterproof. The whole wall/roof assembly will be over R-50 (that’s a real testable R-value, not a grand claim). The additional benefit of wood fiber is the relatively high thermal massHeavy, high-heat-capacity material that can absorb and store a significant amount of heat; used in passive solar heating to keep the house warm at night. , which will make the house cooler in summer. This will be particularly important in the roof. Finally, it is also airtight but vapor-permeable.
Most of the exterior insulation is wood fiber panels imported from Germany. It's applied in two layers over the roof and exterior walls.
However, due to the logistics and costs of transporting such bulky material, it was only cost-effective to get a single 40-foot container of insulation shipped from Germany. This left us with a shortfall of some 50 square meters (about 540 square feet) in the inner layer. The question was what to use to make up the shortfall, and where it would go. We considered various options, including:
Buying more wood fiber insulation from a Canadian supplier. This was rejected because we are short of funds, and it would have cost about three times as much as from the German supplier, even including the costs of shipping. In any case, this would also be imported. We are left wondering, once again, why Canadian companies can’t (or don’t) make competitively priced, high-performing and sustainable wood-based products in a country which has so much timber.
Framing about two-thirds of one of the larger walls and using Roxul mineral wool batts or something similar. However, having specifically built a house that does not have conventional framing, it seemed silly to have to use it non-structurally for the insulation. We’d also had to have made Larsen trusses to avoid thermal bridgingHeat flow that occurs across more conductive components in an otherwise well-insulated material, resulting in disproportionately significant heat loss. For example, steel studs in an insulated wall dramatically reduce the overall energy performance of the wall, because of thermal bridging through the steel. . It just seemed like a lot of extra time and effort. Note that we are not against Larsen trusses at all in general; they are a great solution if you are going to build a highly insulated stick-framed house.
More expanded polystyrene (EPSExpanded polystyrene. Type of rigid foam insulation that, unlike extruded polystyrene (XPS), does not contain ozone-depleting HCFCs. EPS frequently has a high recycled content. Its vapor permeability is higher and its R-value lower than XPS insulation. EPS insulation is classified by type: Type I is lowest in density and strength and Type X is highest.) panels, as we used in the foundation. EPS is not the most environmentally friendly substance, but its better than extruded polystyrene (XPSExtruded polystyrene. Highly insulating, water-resistant rigid foam insulation that is widely used above and below grade, such as on exterior walls and underneath concrete floor slabs. In North America, XPS is made with ozone-depleting HCFC-142b. XPS has higher density and R-value and lower vapor permeability than EPS rigid insulation.) and it actually has relatively low embodied energyEnergy that goes into making a product; includes energy required for growth, extraction, and transportation of the raw material as well as manufacture, packaging, and transportation of the finished product. Embodied energy is often used to measure ecological cost. because it is mostly air. It insulates very well (Type II has an R-value of near 4 per inch). Also, you can get EPS panels cut to the exact size you want, relatively cheaply. There are some disadvantages: it doesn’t have a high thermal mass compared to other materials and it is relatively vapor-impermeable (although still highly airtight). This would make EPS a bad choice for the roof, but using it as a base layer for the wall insulation, all around the house, would not be so bad, because the vapor would still be able permeate upwards through the whole of the rest of the walls and roof. Two rows of 2-by-8-foot panels 9 1/2 inches thick Styrorail, which provided our foundation insulation, would be enough to make up the shortfall.
So that’s what we decided to do. And it is so easy to work with, it was pretty much done in an afternoon. One potential issue was what to do if water was somehow trapped behind the panels, so to cope with that unlikely eventuality, we cut tiny channels in the base of the panels. And it isn’t at all affected by the snow which, right now, is rather important.
Window trim and wall insulation
Window trim might sound merely cosmetic, but it is very important in creating a watertight shell, and with this kind of construction it is even more complex and important than normal. Finishing the windows and the wall insulation are jobs that go together.
We might have installed the windows a while back but, really, that was only the first stage. With 11 inches of insulation butting up against the windows and extending out beyond them, there was substantial work to be done in coming up with and implementing the most waterproof and airtight trim. The best and most cost-effective solution turned out to be renting an aluminum bending machine (also called a "brake") and using it to make our own custom trim from rolls of aluminum. The aluminum trim is fitted over a wooden outer frame. We went for a neutral color that matched the sills we’d already had made.
Despite what the windows may have looked like earlier in the process — and we installed them as far out as they safely could be — they will end up being set quite deeply into the fully insulated walls. There were two potential disadvantages to this. First, it would reduce the solar gain, but Malcolm Isaacs at Construction Maison Passive has done the calculations and we’re okay.
Second, we would see less of the lovely red window frames than we might otherwise have been able to. That turned out to be unavoidable where we have non-opening windows (i.e. four out of the five big ones on the south side), but otherwise the color will still be strong. Because we were able to bend the aluminum any way we wanted, Chris, our builder, has been able to eliminate the need for any extra siding trim (which tends to be much more expensive than siding itself) around the windows: the aluminum will serve multiple purposes.
The crew is now pressing ahead with both window trim and wall insulation, with the most difficult south side being done first. Here, not only do the insulation blocks have to fit around the largest windows and the biggest door, but they also have to fit around the supports for the porch roof.
Tags: , , , , ,
Image Credits:
  1. All photos: David Murakami Wood
1.
Dec 29, 2016 12:43 PM ET
Roof framing
by Malcolm Taylor
For a house with otherwise continuous insulation, don't the applied rafter tails represent a substantial thermal bridge?
2.
Dec 30, 2016 7:05 PM ET
Roof Framing
Possibly, Malcolm. The rafters don't bridge to the outside - they are covered by the outer layer of insulation - and we were advised that according the PHPP calculations, it doesn't make a huge difference. However I'm not entirely convinced - having portions of the edge of the roof which are essentially just over 14" of solid wood and only 1 1/2" of insulation must make some difference. So it's something I am going to be keeping an eye on. My instinct is to add some more insulation inside the CLT roof in the attic space under the rafters. The tight corners under the eaves are basically unusable for any other purpose anyway, so it wouldn't reduce the potential utility of the space up there by very much.
3.
Dec 31, 2016 10:13 AM ET
Rafter tails
by Charlie Sullivan
David, I think Malcolm was referring to the rafters sticking out for the overhang, past the insulation. Those are the tails, which are completely open to the cold outside air. Adding some insulation to the underside, especially near the eaves sounds like a good idea, although where it is most needed is also where you have the least space available.
4.
Dec 31, 2016 7:15 PM ET
Rafter tails
Oh yes, of course... I didn't read it carefully enough. Interesting point. I will have to ask the rest of the team.
5.
Jan 25, 2017 11:47 PM ET
Timber thermal bridge
by Scott Benson Climate Zone 7A
What's the compressive strength of this insulation? Would it be possible to place rafter tails overtop? I have a similar plan in mind and would like to use 12" of the high density roxul on the roof and then frame a structure of 4x4 pine overtop to support overhang
6.
Feb 16, 2017 8:53 PM ET
Rafter tails and thermal bridging
Okay, so I've had conversations with various people involved in the design and build. The short answer is that yes, the rafter tails are inevitably thermal bridges in a limited way. Remember that they will still have an R value of something like 1 / inch. There will be some points at which the distance between the inside of the CLT roof / wall and the nearest outside edge of the rafter that is exposed to the air is less than 20" and therefore the R value at those particular points is at most ⅓ of the R value of the rest of the roof / wall assembly. That's still far more than any window (even passive house standard triple-glazed windows), so we can get a bit too precious about some of this. The exact calculations are all included in the modelling of the building performance, and we can tell you in practice that the house can maintain a consistent internal temperature of 16-18ºC on the coldest days here in Ontario (-25ºC), with no supplementary heating input - so it works. Could it have been better? Yes. Undoubtedly. If we were starting again we probably wouldn't do it this way - we probably wouldn't do many things the same way. However, living in the house is a wonderful experience so we don't have any regrets. Could we do anything to make it better now? Yes, and we probably will - one thing, would be to add extra insulation to the most unusable parts of the triangular eaves inside the attic and we may well do that. In answer to Scott, I am not sure - we haven't investigated the structural / weight-bearing performance of Roxul, however that seems like a much lighter solution, provided the roof on top will be similarly light weight. I would also observe that I've seen a number of very good passive house designs that dispense with overhangs and using roofs for shading and base their shading strategy entirely on various kinds of blinds and louvres - see, for example, the architecture firm, G.O. Logic, of Maine.