Helpful? 0
Why Is This Sheathing Moldy?
A Seattle homeowner finds damp and moldy stud cavities and wants to correct the problem before re-insulating and adding drywall
Posted on Dec 16 2013 by Scott Gibson
Brian Lent has discovered something in his walls that no homeowner wants to see: mold.
Preparing a ground-floor room for drywall, Lent pulls some fiberglass batt insulationInsulation, usually of fiberglass or mineral wool and often faced with paper, typically installed between studs in walls and between joists in ceiling cavities. Correct installation is crucial to performance. from a 2x6 stud cavity and notices the back side of the OSB sheathingMaterial, usually plywood or oriented strand board (OSB), but sometimes wooden boards, installed on the exterior of wall studs, rafters, or roof trusses; siding or roofing installed on the sheathing—sometimes over strapping to create a rainscreen. is damp. A moisture meter reveals that in 80% of the bay, the moisture content is 66% or higher. Moisture and mold are heaviest at the bottom of each bay.
“Interestingly,” he writes in a Q&A post at GreenBuildingAdvisor, “after a panicked weekend a few days ago thinking we had an exterior leak, and much research on the internet and from GreenBuildingAdvisor, came to the consensus that it's a cold sheathing condensation problem.”
His house is in the hills of Seattle, where winters are slightly colder than they would be downtown. The 400-square-foot room in which Lent is working is really a half-basement. It had been left unfinished and was serving as a mechanical room for HVAC(Heating, ventilation, and air conditioning). Collectively, the mechanical systems that heat, ventilate, and cool a building. equipment, including a furnace with an attached humidifier, and two gas hot-water heaters along with two 8-inch duct supplying outside air. He also discloses that he's been running a humidifier during the winter to make indoor air more comfortable.
His remediation plan, already underway, includes killing the mold with a disinfectant, drying out the materials with heat and dehumidification, and then reinstalling the R-19 batts. He’ll finish the walls with mold-resistant drywall, a primer, and two coats of latex paint.
Is he on the right track? Or is there something missing from this equation? That’s the focus of this Q&A Spotlight.
The humidifier is a big mistake
Indoor relative humidity in his area should average about 30% at 70 degrees F during the winter, writes Dana Dorsett. “The only way you would ever need to add humidity is if you were ventilating at ridiculous rates during the middle of a cold snap,” he says.
If the relative humidity is 50% at 70 degrees, the dew point is about 51 degrees, Dorsett adds, but the mean temperature at Lent’s elevation of 800 feet is about 39 degrees. The result? “The cold sheathing is going to take on significant amounts of moisture.”
He suggests limiting indoor relative humidity to no more than 35%.
Running a humidifier, says GBAGreenBuildingAdvisor.com senior editor Martin Holladay, “is always a mistake.” Should the air inside a house get too dry in winter, it’s usually a sign that the house has a lot of air leaks. The solution, he says, is to plug them — a task that is made easier with the help of a blower door.
“Once you have lowered the humidity of the room, and once you have convinced all of the members of your family of the importance of destroying your humidifier with a sledgehammer, you should probably consider insulating these problematic stud bays with closed-cell spray polyurethane foam,” Holladay says. “The foam will provide an effective air barrierBuilding assembly components that work as a system to restrict air flow through the building envelope. Air barriers may or may not act as a vapor barrier. The air barrier can be on the exterior, the interior of the assembly, or both. to prevent the interior air from contacting the cold OSB.”
Other insulation options
While effective, spray polyurethane foam is an expensive insulation option, and Lent wonders whether he’ll have to pay a premium to interest an insulation contractor in such a small job.
There are a couple of other options, as Dorsett points out:
  • Blown-in cellulose. Cellulose has the capacity to pick up some of the moisture to become a buffer, and the borateBoron-containing chemical that provides fire resistance to materials such as cellulose insulation and provides decay and termite resistance to wood products. Borate is derived from the mineral borax and is benign, compared with most other wood treatments. fire retardants used in cellulose insulationThermal insulation made from recycled newspaper or other wastepaper; often treated with borates for fire and insect protection. are effective against mold and fungus. Further, Doresett says, “The air-retardancy of cellulose even at 2-lb. density is about 90% better than that of low-density fiberglass, (at 3-lbs+ density it's about 99% more air-retardant), nearly eliminating the convective transfer of moisture from the interior side to the exterior.”
  • Rock wool batts. When installed perfectl, rock wool batts block air nearly as well as 2-lb. cellulose, Dorsett says, and have an R-valueMeasure of resistance to heat flow; the higher the R-value, the lower the heat loss. The inverse of U-factor. of 23.
  • Double up the batts. Compress both unfaced R-13 batts and the original R-19 batts into the stud cavities for an R-20 to R-21 wall.
  • Flash-and-batt. Spray in an inch of foam as an air sealing layer and vapor retarder on the interior side the OSB sheathing, and then compress the old R-19 batts on top of the foam.
Now, about that ventilation system
Lent wrote that he planned to connect the two 8-inch-diamter passive outdoor air ducts to his furnace's forced-air distribution system. Holladay responded that this move would make the house “wildly over-ventilated (and dry).”
“If you want to install this type of ventilation system — called a central-fan-integrated supply ventilation system — you need to include a FanCycler control, and you need to include motorized dampers and a commissioningProcess of testing a home after a construction or renovation project to ensure that all of the home's systems are operating correctly and at maximum efficiency. process that verifies the air flow,” Holladay writes. He suggests Lent have a look at a blog on the topic.
Lent replies that he has already installed a FanCycler control, and that he’s programmed the control to stay open as much as the software will permit, 50% of a 24-hour period.
“However,” he adds, “the concern that is not addressed in that document is coordinated timing: there is no guarantee that when systems that evacuate internal air (i.e., bathroom fan during a shower, whole-house fan, cooktop) the external damper via the FanCycler will be open. Thus, we can’t ensure the house will be consistently positively pressurized. So, the proposal is to always be pulling some amount of outside air into the central system (at the expense of increased energy consumption, understood).”
Dorsett writes that ventilating a house with a furnace is a “common but pretty lousy way to go about it, since you only get the ventilation when it’s running and the ventilation rates go up when you least want it (when the outdoor air is colder and drier).”
Aaron Birkland says the ideal airflow rate for a FanCycler must be calculated to match the house, taking many factors into consideration. The goal should be to open the outside damper for a certain amount of time per hour while the air handler is running; and also to make the air handler run for a certain length of time each hour if it won’t do so naturally.
“As you can see, it's intended more as a means to meet a specified target level of ventilation, rather than provide constant positive pressure to the house,” Birkland writes. “The fact that it does induce a small degree of positive pressure is a side effect of how it happens to operate, rather than a design feature. So opening the supply vents or adjusting the programming to force lots of outside air is kind of a bad thing.
“It will lead to over-ventilation, and won't really do anything useful or consistent as pressurizing the house goes,” he adds. “I'd say it's best to just calculate the ‘right’ level of ventilation for your house, and program the FanCycler to aim for that.”
Our expert’s opinion
GBA Technical Director Peter Yost added these thoughts:
It’s great that Brian Lent found GBA in time to understand how his exterior walls got moldy. GBA emphasizes the importance of a continuous air barrier on those same exterior walls. That is the real way to keep these walls dry after his rework of the walls is done. As Martin Holladay noted in his first answer to Lent's questions, "Plug the air leaks. ... Consider insulating these problematic stud bays with closed-cell spray polyurethane foam."
While it’s true that cellulose is a lot more airtight than fiberglass batts, it’s not anywhere near tight enough to be the dedicated air barrier. Flash and batt or the airtight drywall approach is the way to go while Brian has the opportunity.
And that same continuous air barrier will improve or eliminate wintertime dryness issues. I never have found a home in which wintertime dryness was not the result of either air leakage or overventilation.
Building America research done quite some time ago at Building Science Corporation shows that the positive pressure associated with Central Fan Integrated Supply (CFIS) ventilation is very slight, in the range of no more than 3 Pa. And that positive pressure is intermittent as well. Sure, there are more sophisticated mechanical ventilation systems than CFIS, but it does deliver fresh air and distribution of that fresh air as well. Martin’s blog referenced above does a thorough and fair job of assessing the different approaches to residential mechanical ventilation, including CFIS.
Tags: , , , , , ,
Image Credits:
  1. Brian Lent
1.
Mon, 12/16/2013 - 11:27
on the RH% subject..
by Jin Kazama
Helpful? 0
I have noticed a growing mass of malinformed homeowners thinking that low RH% is bad for health.
Problem is they are seeking 40-50% RH during winter time, which is obviously not necessary at all.
There is no problem associated with 30-35%RH @ 20c and human health.
RH% and homeowning is another thing that should be teached at schools to the 12-16old
to prepare them for their life.
I have yet to see a "recent" house go down below 25%RH during winter time if it kept @ ~21c .
If i recall correctly, 20%RH starts posing health concerns @ ~12c ?? but who wants 12c .
So prepare for more " humidifier" "desastres" in the coming years.
2.
Mon, 12/16/2013 - 22:04
Seems to me like an option
by Alexandre Richer
Helpful? 0
Seems to me like an option would have been to use some "hipster membrane" that acts as an air barrier, and fill the bay behind it with high density cellulose.
3.
Tue, 12/17/2013 - 05:21
Response to Alexandre Richer
Helpful? 0
Alexandre,
Filling the stud bays with an air-permeable insulation, as you suggest, will not address the underlying problems. And experience shows that an interior membrane is insufficient to prevent the moisture in a home's interior air from reaching the cold side of a wall assembly.
Here's one way to look at it: the air between the pieces of cellulose is interior air, not magic dessicated air. That air contains moisture, and it is in contact with the sheathing.
Moreover, changes in temperature create a pumping action which results in air exchange between the interior and the air between the studs. On cold nights, the air between the studs contracts, and on hot afternoons, the air between the studs expands. Your "hipster membrane" will not prevent this pumping action, which tends to bring more interior air (and therefore moisture) into the stud bays.
The remedy, as I suggested before, is (a) to lower the indoor relative humidity by getting rid of the humidifier, (b) to allow the sheathing to dry, and (c) to create an exterior air barrier against the sheathing with closed-cell spray foam.
4.
Tue, 12/17/2013 - 11:41
Edited Tue, 12/17/2013 - 11:45.
Response to Martin Holladay
by Ron Keagle
Helpful? 0
Martin,
Regarding your points in post #3:
I am not sure what Alexandre meant by “hipster membrane.” If he was referring only to a netting to hold the cellulose, I can understand why that would not solve the moisture problem. But if he was referring to a smart vapor retarder, why wouldn’t that prevent the vapor from condensing on the cold sheathing by simply preventing the vapor from entering the wall in the first place? Or; why wouldn’t the airtight drywall technique solve the problem? It would eliminate the air leaks transporting vapor into the wall cavity and the effect of diffusion would not be significant enough to matter.
I agree that the main cause of the problem experienced by Brian Lent is excess indoor humidity. Secondarily, as I understand it, he also had no drywall or vapor retarder installed as the problem developed. In reading his planned remedy, I don’t see that reducing the humidity is part of it. He mentions his plan to finish with mold resistant drywall that is primed and painted with two coats of latex paint.
I would add to that prescription, the reduction of indoor humidity and a smart vapor retarder properly installed between the studs and the drywall. An alternative to the vapor retarder would be airtight drywall. If I had to choose one or the other, I would choose the vapor retarder, but I would also make the drywall nearly airtight as a matter of course. I don’t see mold resistant drywall or painting as being part of the solution in dealing directly with vapor transmission and wetting.
5.
Tue, 12/17/2013 - 12:15
Response to Ron Keagle
Helpful? 0
Ron,
Brian Lent's wall is a mess. He wants to fix the wall once and for all, so that when it is all buttoned up, he doesn't have to worry about the problem recurring. This is not a situation that calls for half-measures.
The most important moisture transport mechanism at work here is air leakage. If the new drywall is installed using the Airtight Drywall Approach, that will go a long ways towards solving the problem, as you suggest. But it still leaves cold OSB sheathing, and Brian Lent doesn't want to see any moldy OSB again.
So while it is possible -- perhaps even probable -- that cellulose plus the Airtight Drywall Approach might solve this problem, I still advise Brian to invest in spray foam. The spray foam will stop air leakage and warm up the first condensing surface in the stud bays. The foam will help Brian sleep at night.
6.
Tue, 12/17/2013 - 14:04
Hipsterism.
by Alexandre Richer
Helpful? 0
By "hipster membrane" I do mean the "smart", usually European, vapour retarders like those sold by foursevenfive in Brooklyn and Small Planet Workshop in Washington State. I agree that spray foam will provide better peace of mind in this instance.
7.
Tue, 12/17/2013 - 14:12
Helpful? 0
Alexandre,
"Hipster membrane" is useful shorthand. I may adopt the term. Thanks.
8.
Tue, 12/17/2013 - 16:04
Smart vapor barriers are fairly vapor open at 50% RH
by Dana Dorsett
Helpful? 0
The wintertime humidity isn't super-low in that climate, and if they continue to actively humidify to 50% relative humidity a smart vapor retarder would be no more vapor retardent than latex paint. Only when the RH is under 35% does it drop to class-II vapor retardency. Smart vapor retarders CAN be used to good effect in that region, but not in actively humidified homes.
This experimental test done by Washington State University at their Puyallup WA test facility (southern Puget Sound region) demonstrates the efficacy of Certainteed MemBrain in that climate:
http://www.energy.wsu.edu/documents/AHT_ComparingTheMoisturePerformance%...
9.
Wed, 12/18/2013 - 20:55
Confused
by L H
Helpful? 0
This subject has really piqued my curiosity. I've always been told that the reason to humidify is because winter air, being colder, is drier and that heating dries it out further.
I do not humidify because I agree that it's a bad idea, but the people I know who do use a humidifier do so because they are suffering from dry skin, chapped lips, and breathing problems like asthma, that are aggravated by drier air. I know that parents of infants are often advised by doctors to humidify, particularly during bouts with respiratory infections. Can you explain further about this issue?
10.
Thu, 12/19/2013 - 07:45
Response to L.H.
Helpful? 0
L.H.,
There are two components to your question:
1. Does dry indoor air really cause medical problems?
2. What is the best way to raise indoor relative humidity during the winter?
On the first question, I defer to medical professionals. Here's my perspective, however: dry air irritates some, but not all, people. Remember, the outdoor air in a desert climate is often extremely dry, and people have been living in these types of climates for tens of thousands of years. Many Americans move to the Southwest because the dry air is said to be good for their health.
On the second question, here's my advice: if the indoor relative humidity (RH) in your home is too low during the winter, the solution is to seal the air leaks in your home. If you try to solve the problem by installing a humidifier, you risk causing moisture damage to your home.
Leaky homes obviously have a high air exchange rate. All of that outdoor air is extremely dry during the winter, so high rates of air infiltration result in low indoor RH. Plug the air leaks, and you will solve the problem.
For more information on the necessary steps, see:
Air Sealing an Attic
Air-Sealing a Basement
11.
Fri, 12/20/2013 - 11:11
Relative humidity set point
by John Hunter
Helpful? 0
Several commenters have suggested that winter time RH should be in the mid-30s. Clearly, keeping RH at that level does help prevent mold growth and prevent condensation on window glass. However, despite what some have said, that level of RH can be unhealthy for occupants of the home, leading to problems such as dry skin, nose bleed, and worsening of asthma symptoms (all of which my wife and I have experienced when the RH has been low). We keep our humidistat set at 45% year round and have found that we don't have any of the symptoms I just cited, nor have we found any mold anywhere in the house. Also, we have found that anything lower than 45% can lead to problems with our antiques and works of art. We have a humidifier on the HVAC return air plenum and we run a portable dehumidifer in the summer when needed. We are located in Northern Virginia.
12.
Fri, 12/20/2013 - 14:39
Controlling Humidity
by Ron Keagle
Helpful? 0
I would want to build a wall that did not require limiting the indoor humidity for the purpose of preventing wetting inside of the wall cavity. Then I would only limit indoor humidity to the extent needed to avoid window damage.
13.
Fri, 12/20/2013 - 18:45
Heating the air does not dry it out (response to L.H.)
by Dana Dorsett
Helpful? 0
There is nothing about a heating system that removes moisture from the air. Ducted hot air systems can sometimes increase the infilatration rate (unintended ventilation through leaks in your house) which can reduce the moisture levels of the indoor air, but that's an air leak problem (as Martin suggests), not a heating problem.
Taking cold air as some nominal relative humidity and heating it to a higher temp changes it's relative humidity, but that's the "relative" part. At the same moisture content raising the temperature of the air raises the amount of moisture necessary to saturate/condense (100% humidity== fog conditions).
Since human activities such a breathing, bathing, cooking, watering the houseplants etc all contribute moisture to the interior air, in a fully air-tight house moisture levels will rise over time to unhealthful levels (for both you AND the house.) The widely prescribed "healthy" air levels for humans from the medical professionals is 30-50% RH @ 68-75F indoor temps.
But while 50% RH @ 70F is OK for YOU, the "dew point" of that air (the temperature at which it's relative humidity = 100%) is about 51F, which means if your wintertime outdoor temperature averages are in the 40s or lower, the sheathing is colder than the indoor dew point, and can adsorb considerable moisture content even via vapor diffusion through the wall, unless there is a sufficiently vapor retardent layer to control the rate of moisture flow. (Air leaks from the interior are even worse, MUCH worse than vapor diffusion transfer.) If instead you control the interior RH to a limit of 35% @ 70F it's still healthy for the humans, and the dew point is then 41F, which is below the mean wintertime outdoor temps in the Puget Sound area, but still above the wintertime mean temps of climate zone 5 locations.
The solutions for those colder locations is varied. The standard 1980s solution was to put an interior side vapor barrier up, but those have proved problematic in practice due to air-leakage and summertime moisture drives from the exterior (particularly on brick or stucco homes.) Another is to build in a ventilated gap between the siding and sheathing that alone is sufficiently protective for a zone 5 location, since the drying rate toward the exterior mostly keeps up, and when temps are warmer, the drying rate is fairly rapid. Another solution is to add sufficient R value on the exterior of the sheathing to bring the mean temp of the sheathing high enough that it doesn't take on too much moisture. These solutions are now enshrined in IRC building code, broken down by US climate zone:
http://publicecodes.cyberregs.com/icod/irc/2012/icod_irc_2012_7_sec002_p...
But these solutions do NOT all work if you are dumping a ton of moisture into the house, keeping it at 50% RH!
14.
Tue, 12/24/2013 - 01:02
Hipster Membrane?
by albert rooks
Helpful? 0
Perhaps I'm not aware of the age limits involved but I feel to old to be a "hipster".
And Siga Majpell doesn't quite fit the "hip-ness" of the product classification. It's got a low perm rate fixed in Class II (0.68 US Perms). It's the interior high humidity conditions like this one that point out where a Class II fixed rate is really useful.
Hipster or not, Yes, it's the air leakage and not the diffusion that are the most important issue to deal with.
Happy Holidays from The Small Planet Workshop.
Become a GBA PRO!